A always note it on an EICR if there is no appliance isolators
If I want to prove a point I download the installation manual for the appliance - these almost always state an isolator with a 3mm DP contact switch is required.
As manufacturers instructions over ride the regulations then it is a warranted observation.
IIRC it says something on the onsite guide about appliance isolators in kitchens , but I cant be bothered to go to the van as it is raining outside (book in van)
 
I don’t believe Manufacturer’s instructions do override the Regs.
I think you’ll find it’s back to being taken account of?
 
I have not got the new regs to hand (office needs a tidy)
The previous regs had
Section 134 ERECTION AND INITIAL VERIFICATION OF ELECTRICAL INSTALLATIONS
134.1 Erection
Regulation 134.1.1Good workmanship by competent persons or persons under their supervision and proper materials shall be used in the erection of the electrical installation, Electrical equipment shall be installed in accordance with the instructions provided by the manufacturer of the equipment.

PART 5 SELECTION AND ERECTION OF EQUIPMENT
CHAPTER 51 COMMON RULES
510.3 Every item of equipment shall shall be selected and erected so as to allow compliance with the regulations stated in this chapter and the relevant regulations in other parts of BS7671 and shall take account of manufacturers' instructions.
 