I got a call from a lad who runs a snack shop asking why his fuse kept 32 amp fuse kept tripping . I went to the shop to have a look he has a total of 20000 watts (100 amps )on at one time with fryers, hot plates ,grills etc ! All single phase . Having little experience myself as a spark I would say he needs 3 phase ? Can any lads give me advice
 
You can probably manage to run a potential total 100A load quite readily on a 100A supply fuse.
The circuits may need to be appropriately split up to even out the load on any one breaker.
If the maximum total demand is in excess of 100A then a three phase supply would be indicated.
However cost wise it may be cheaper to rationalise the loading and ensure that the maximum demand is not over 100A.
 
Last edited:
You can probably manage to run a potential total 100A load quite readily on a 100A supply fuse.
The circuits may need to be appropraitely split up to even out the load on any one breaker.
If the maximum total demand is in excess of 100A then a three phase supply would be indicated.
However cost wise it may be cheaper to rationalise the loading and ensure that the maximum demand is not over 100A.

I would need to check the main fuse size as I replaced a main fuse few weeks ago in a house which had blown caused by short circuit, when I opened the cartridge up I found it was a 63 amp fuse
Thanks for the reply Richard
 
I got a call from a lad who runs a snack shop asking why his fuse kept 32 amp fuse kept tripping . I went to the shop to have a look he has a total of 20000 watts (100 amps )on at one time with fryers, hot plates ,grills etc ! All single phase . Having little experience myself as a spark I would say he needs 3 phase ? Can any lads give me advice

Unless you establish what is connected to said 32A MCB you won't make any progress. The 100A total may not be relevant but useful to know.
 
Hi Bosun, if your friend has been frying this circuit for a while (gradually adding load till it pops, resetting, go again etc) then I suspect the MCB may also be cooked. So, along with the works to distribute load across other circuits I would replace this MCB.
 
Hi Bosun, if your friend has been frying this circuit for a while (gradually adding load till it pops, resetting, go again etc) then I suspect the MCB may also be cooked. So, along with the works to distribute load across other circuits I would replace this MCB.
Thanks wilko for the advice
 

Reply to Overload or what ? in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Some advise or views would be appreciated. My supply is 100 amp single phase. I purchased my property 3 years ago or so, the owner prior to the...
Replies
29
Views
795
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock