some advice would be greatly appreciated

i was under the impression that pc monitors were class 2 yet i am unable to confirm this with the double square logo on some monitors a customer has asked me to check, should they be treated as class1 or 2 ?

also slightly unsure on permisable earth leakage test limits / results
book of words say 0.25 mA but the few i have tested all showed about 0.40mA which is still minute but apparently fails
would really appreciate some help please

using a seaward 250
 
Earth bond @ 100mA, insulation @ 500v NO earth leakage. Earth can be picked up on visible chassis at rear or via shell of RGB plug.
 
PC equipment, generally a visual. With monitors you often won't have access to exposed metal parts. Insulation and load test could cause damage to the switch mode supplies unless you test with 250v bear this in mind. Earth leakage can vary.
 
thanks Gents]
when you say no leakage test, I take it you mean runs test ( starts up for 5 seconds)
my machine does a leakage test with out starting it up i think its called a substitute leakage test, should i interrupt the testing after the earth bond and I/R test?
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
pc monitors
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
3

Thread Tags

Advert

Thread statistics

Created
morph,
Last reply from
morph,
Replies
3
Views
1,935

Advert

Back
Top