Hi Ian,Assume that the main supply is upstairs in the airing cupboard together with the clock,vave(s) etc. There is just a t/e running down to the boiler. Clever heating firm come along and fit an Icos boiler that needs a perm live or a back boiler that has lights in the front or electronic ign for the gas fire.
Normally i insist that a new 3 core/earth is installed, but tomorrow,s job apparently that ain,t gonna happen!
They reckon i should fit a 3 pole switch with the switced live and neutral then spur off a local socket for the perm live taking that through the 3rd terminal of the 3 pole. Phew! The 3 pole would then give means of isolation at the boiler but there would still be 2 different supplies at the boiler.
Ian
I recon your easiest way out would be to ensure that you have volt free contacts at the timeclock/programmer,then take out the link,then arrange it so that your t&e going to boiler would
be your switchwires(COMING from and going back to boiler)instead of your neutral which would now be coming from your new local boiler supply.You could then fit a caution label at programmer (fed from 2 sources)But maybe too late and you've the job done