Discuss Permanent live to a boiler in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Assume that the main supply is upstairs in the airing cupboard together with the clock,vave(s) etc. There is just a t/e running down to the boiler. Clever heating firm come along and fit an Icos boiler that needs a perm live or a back boiler that has lights in the front or electronic ign for the gas fire.
Normally i insist that a new 3 core/earth is installed, but tomorrow,s job apparently that ain,t gonna happen!
They reckon i should fit a 3 pole switch with the switced live and neutral then spur off a local socket for the perm live taking that through the 3rd terminal of the 3 pole. Phew! The 3 pole would then give means of isolation at the boiler but there would still be 2 different supplies at the boiler.

Ian
Hi Ian,
I recon your easiest way out would be to ensure that you have volt free contacts at the timeclock/programmer,then take out the link,then arrange it so that your t&e going to boiler would
be your switchwires(COMING from and going back to boiler)instead of your neutral which would now be coming from your new local boiler supply.You could then fit a caution label at programmer (fed from 2 sources)But maybe too late and you've the job done
 
That would work mrloy99 if the valves and pump were by the boiler, if not you have the same problem.
A feed from the boiler after going through the time clock would need to open a valve and start the pump, both of these need a neutral.
 
That would work mrloy99 if the valves and pump were by the boiler, if not you have the same problem.
A feed from the boiler after going through the time clock would need to open a valve and start the pump, both of these need a neutral.
I suppose you would need to see the full set up,but maybe at the board the two circuits could be put
into one breaker to keep it all on one circuit,then at least the whole lot could be isolated there in one go.
 
Hey Ian.

If you've already done the job then ignore this.

I came across this exact situation only about 3 weeks ago.

I had a phone call from one of the kitchen staff in the school where I had been working to say the all the little red neons on her switched fused spurs in her kitchen wouldn't go off.:confused:

When I got there the first thing I noticed in the corner of the kitchen was a shiny new worcester boiler which a large Anglo Fossil Fuel company had that very day installed.:rolleyes:

Sure enough no matter what way the switches on the spurs were, the neons stayed on, never done that before she said:confused:

Anyway I'm going off on one here so to cut a long story short BG had spurred off the kitchen ring to feed this new boiler as there was only the T+E coming down from the wiring center in the airing cupboard. Now all was fine as long as the boiler spur was turned on but when she turned this off thus removing perm live supply to boiler all the neons in the spurs lit up.

Reason - switched live still present from timer upstairs running through boiler and out via prem live supply backfeeding (only a small amount of voltage) onto kitchen ring.;)

Moral of the story install new 3c+cpc.:D
 

Reply to Permanent live to a boiler in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I had to wire in an extra 2 port valve today to protect a newly installed unvented cylinder (replacing the old gravity fed one) in a standard Y...
Replies
12
Views
2K
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
I went to look at mess this morning. S plan heating system, google nest heat link in airing cupboard. Downstairs in utility room the kitchen...
Replies
5
Views
800
At the moment it depends on the weather on how well the central heating works, the main problem is the Nest Gen 3 thermostat only measures the...
Replies
7
Views
715
Hello, I hope you are well, I have fitted a few Nests but only to Combi, S and Y plan systems just been looking a job where I’m doing the kitchen...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock