M

mat_12345

I'd taken a socket faceplate off to do some decorating but after putting it back, the MCB was tripping and tripped every time I tried to reset it. After taking the cover back off (wires still connected), it didn't trip.

Looking at it - maybe one of the wires was getting pinched by a screws - it looks like it has been pinched at some point, though nothing has gone as far as to expose the wire.

I used a 10mm spacer to give the wires more room and it seems OK now. Do I need to do anything about the wire that was pinched? There's a wee bit of blackening too, on the back box and on the wire.
 
A few pics may help but if it has pinched the wire resulting in the protective device tripping then the copper has been exposed. It there are black deposits on the conductor and back box then a line to earth short has taken place and it definitely needs looking at.
What is a 10mm spacer?
 
  • Like
Reactions: Jim_e_Jib
One of these, im guessing....

 
Yeah one of those.

Thanks, I'm going to get someone out.

Just for my understanding, what's a line to earth fault?

Also - this may / may not be relevant, but in all the resetting the MCB, I left it on at one point and got a shock when I first went to put the spacer on (I know - I'm an idiot). I don't think that caused the blackening, but could it?
 
I should have said live to earth fault, red or brown wire being live and the back box earth.
If you got a shock you must have been in contact with a live part and earth or neutral.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Pinched wire (but copper not exposed) - leave or fix?
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
mat_12345,
Last reply from
westward10,
Replies
4
Views
1,872

Advert