I have a couple of questions regarding a PIR today
TT , with a 16th board fitted (1 RCD protecting Sockets)
1. The oil line is plastic apart from a 500mm length where it joins the fire v/v then into the property, does this small section need to be bonded??
2. There are two mcbs supplying sockets
- first has 6x 2.5's in it. (2 rings and 1 radial)
- Second has 4x 2.5's in it (2rings)
3. All the neutrals in the RCD side of the neutral bar are not in the correct terminals
4. Property has a Ze (of 128ohms) but can't find the rod anywhere. (code 3)
There is also some phone cabling that has been chewed by a dog and taped up.
Appreciate some guidance on how to code this lot
Thanks for your help
G
1, not sure but I would err on the side of caution and bond it just in case. Code2
2, Not incorrect but bad practise, also would advise need for a new CU to segregate circuits in the event of a fault. Code2
3, this practice is just sloppy but not a defect as such, new CU would fix this if installed correctly. Additional info/recommendations
4, you need to find or fit a rod or enquire about getting a PME connection, this reading could be due to pipework etc so this is a code 1 in my opinion, as you cannot determine if it has a proper earth. Code1.
Await further replies etc
Cheers........Howard
Thanks Howard,
I could easily separate out some of the circuits as there are 3 spare ways on the RCD side of the board (MK Sentry)
Good idea about enquiring about PME, i'd completely forgot about that
I'll phone western power tomorrow.
Any other takers
G
1 if its no chance of introducing a potential then I would not bond it.
2 not good but happens a lot, code 2 in my opinion.
3 code 2.
4 Don’t do a lot of TT now, but when I did, I regularly could not find the rod, it often had a patio built over, but if you disconnect the bonding to gas water etc and you still get a reasonable reading then I would assume its there and give it a code 2.
ian
Griffin,
ian,