Evening Chaps,
I have a couple of questions regarding a PIR today
TT , with a 16th board fitted (1 RCD protecting Sockets)
1. The oil line is plastic apart from a 500mm length where it joins the fire v/v then into the property, does this small section need to be bonded??
2. There are two mcbs supplying sockets
- first has 6x 2.5's in it. (2 rings and 1 radial)
- Second has 4x 2.5's in it (2rings)
3. All the neutrals in the RCD side of the neutral bar are not in the correct terminals
4. Property has a Ze (of 128ohms) but can't find the rod anywhere. (code 3)
There is also some phone cabling that has been chewed by a dog and taped up.
Appreciate some guidance on how to code this lot
Thanks for your help
G