mogga
hypotheticaly a wooden shed is a temporary structure as there arent any founds so would it need tested every 3 months ?
If done properly with the right csa cable, pd, etc I'd suppose it would be fixed wiring. Saw a good one at an old ladies house once, she had an outside light connected into a single s/o which wasn't connected to the RFC, to power it she had a length of flex with a plug top at both ends. The installer must have been a real credit to our profession![]()
hypotheticaly a wooden shed is a temporary structure as there arent any founds so would it need tested every 3 months ?

My point really is whether a homeowner could unplug it and say "I don't want this testing". Then you would have to note on any documentation that "No circuits or equipment tested which use a plug and socket", be it a brick garage or a shed.
None of it is really 'installed correctly' though - it's not part of the fixed installation because it's got a plug on the end, and it's not an appliance because part of the wiring is fixed down.As said if installed correctly then fixed wire with isolating plug i'd say as it isnt a portable appliance...
None of it is really 'installed correctly' though - it's not part of the fixed installation because it's got a plug on the end, and it's not an appliance because part of the wiring is fixed down.
I think if you wanted to put this kind of wiring into a category it would be 'DIY bodge', kind of like in pubs where there is a plugtop plugged in somewhere, the flex clipped down to the skirting board or up the wall, then disappears off somewhere, quite possibly with another socket on the end.
I do agree with you it isnt a great way to install and not a way I'd ever do it, but just because its got a plug on the end doesnt mean its not fixed wiring, if its all fixed wiring feeding the shed then the plug is just a way of connecting to the mains, it will be classed as a final circuit not portable equipment and so should be tested when testing the fixed wiring.
This is where the edges start to get blurred, which can be dangerous because it gives rise to confusion. An extension lead can be screwed to the wall and the cable clipped down, but that doesn't make it fixed wiring, just the same as if an appliance is wired into a FCU that doesn't stop it being an appliance and should still be PAT tested.I do agree with you it isnt a great way to install and not a way I'd ever do it, but just because its got a plug on the end doesnt mean its not fixed wiring, if its all fixed wiring feeding the shed then the plug is just a way of connecting to the mains, it will be classed as a final circuit not portable equipment and so should be tested when testing the fixed wiring.
This is where the edges start to get blurred, which can be dangerous because it gives rise to confusion. An extension lead can be screwed to the wall and the cable clipped down, but that doesn't make it fixed wiring, just the same as if an appliance is wired into a FCU that doesn't stop it being an appliance and should still be PAT tested.
The best way to avoid confusion is to steer clear of ingenious solutions like this altogether.
I totally agree mate, but still come across them so hard to steer clear of.
nothing wrong with that years ago apparently! I have an old book and it actually shows lighting rigs being made and advises to use a board with a row of 5a sockets on,1 for each lamp and 1 to link to next bank,maybe electricity wasn,t as dangerous back then? lolI found 12 of these backstage in a school as part of the stage lighting system, using them as 'patch leads' amazing......
I think personaly I would list somewhere INCASE some bright DIYer fitted an FCU and should anything happen in the garage then at least you aould have CYA Although I also do not like lloads of limitations notes ect there are times when they make it easier for joeBloggs to understandA periodic inspection is an inspection of the fixed wire installation, you could list plugged in items as an exception but technically you wouldnt even need to.