I have a metal container / cabin with plastic consumer unit c/w RCD main switch and earth electrode, cabin is being supplied by a diesel generator with a bonded neutral located about 10 metres away in its own shed. Customer has tried wiring this up on their own and called me for help when they couldn’t get a voltage reading between live from the genny and the earth from the electrode . Explained that this was due to the ground earth not being referenced to the genny and that the neutral from the genny should probably also be used to Earth the cabin. But here is my question; Is it acceptable to link the neutral and earth bar within the consumer unit or should both the sub main cpc and neutral be commonly connected at the genny end?
Also in addition should there be electrodes driven in and connected at the cabin and/or genny to reference to ground earth too?
Cheers
I have a metal container / cabin with plastic consumer unit c/w RCD main switch and earth electrode, cabin is being supplied by a diesel generator with a bonded neutral located about 10 metres away in its own shed. Customer has tried wiring this up on their own and called me for help when they couldn’t get a voltage reading between live from the genny and the earth from the electrode . Explained that this was due to the ground earth not being referenced to the genny and that the neutral from the genny should probably also be used to Earth the cabin. But here is my question; Is it acceptable to link the neutral and earth bar within the consumer unit or should both the sub main cpc and neutral be commonly connected at the genny end?