I've had boiler pumps causing havoc with RCDs before. But if it was that, it should trip when it tries to run. Does the boiler have an internal pump? If so, it's possible that it wasn't in circuit when you were IR testing perhaps.
 
I've had boiler pumps causing havoc with RCDs before. But if it was that, it should trip when it tries to run. Does the boiler have an internal pump? If so, it's possible that it wasn't in circuit when you were IR testing perhaps.

The Boiler was a Combi boiler ( again less than 8 years old ) with an external potterton 1 channel time clock for the heating.
So when I carried out a Insulation Resistance test i doubt the pump would have been included in the circuit.

If the problem remains I'll stick the link back into the boiler.
To be honest there wasn't a great deal on effected side of the DB.

Upstairs Lights ( no outside lights)
Downstairs Ring ( no outside sockets)
Boiler ( 1 x twin socket in loft, with a TV amp also plugged in)
Smoke Alarms ( 3x Aico, interlinked )

But the boiler has been running pretty much all the time keeping the house at a constant 20 degrees.


ACAD126G.jpg

By the way here's a pic of the damaged lead !
 