So I had my yearly assessment today with my friendly local engineer. He was fair enough but there was 2 points he pulled me on that have niggled me because I am sure I was right.
Would like some other opinions please.
Firstly a 60 Amp TN-S supply to a domestic property. ... what is the minimum size tails?
Secondly do you guys tick the double insulated box in S.O.I because of the meter tails?
I'll let you know who was in each corner after a few replies so as not to sway your decision ( as if it could)
First one depends on the load that you have calculated for the installation.
Second one I don't agree with. Tails are insulated and sheathed, same as twin and earth...
Edit: Speedy Lee beat me to it!
I installed 25mm tails to a db in the garage around 1 meter from meter/cut out.
Was told the db could be hit by a larger car (whatever that means) and I should have moved the db with a switch fuse isolator and coming out to other side of garage with a 35mm swa 2core and 16mm cpc.
I asked my QS why 35mm as volt drop wasn't an issue, he said had better mechanical strength haha!!
Theoretically the minimum size tails for a 60A fuse would be 10mm² as this can take 64A when clipped direct (and tails are often in free air). I would tend to use 16mm² as the fuse may often be 60/80A labelled so I could not be sure of the protective rating.
For the schedule of inspections the protective measure for meter tails is ADS, by chance the cable could be classified as equivalent to double insulated, but the sole protective measure is not double insulation, it is ADS. If if it were double insulation then there would be no fuse required and no earthing required.
Now worried about the quality of the assessors if their reference books are just the OSG.
Double insulation means TWO layers of insulation or a single layer of reinforced insulation so in your case it doesn't apply. Those conductors have one layer of insulation and an overall sheath for mechanical protection.
Need to stand your ground with these people.
16mm tails on existing install... 25mm tails on a new install (both with 60A main fuse)
i.e. I wouldn't upgrade the 16mm tails to 25mm on an existing install with a 60A fuse.
My thoughts on clipped direct is that it may apply between the head and meter where there is no enclosure, enter them into a board they are no longer clipped direct and should be down rated.
No talking of tails, yes they can be clipped direct between head and meter but they are no longer clipped direct within the CU.
That would mean 16mm tails CCC would be 76amps reference method B and maybe couldn't be adequately protected by a DNO 80amp fuse , tho load profile maybe acceptable If clipped direct then 87 amps
The bloke does not know what he is talking about. Lots of sparkys will use 25mm no matter what size the supply cut out is, I will not even up grade tails with a 80 amp cut out. ( you lot may have to depending on installation method)
He actually said it had to be 25mm because the cuu main switch is rated at 100A.
Hi Andy, yes similar nonsense heard once re domestic board with multiple final circuit mcbs (all correctly selected and installed) adding up to over 100A installed capacity. Does my head no good at all.
I did a CU replacement a while back. On of the CU's was for the off peak heating & hot water, it had a 100amp main switch. The off peak meter (Ec 10) had two out puts, and the one for the hot water, would only accept a 10mm cable.
Lol.
Insulated and sheathed tails are deemed as being double insulated.
T&E is not, because the Earth conductor is uninsulated.
ADS is the usual method of protection, as long as the installation is not TT and/or the length of the tails is less than 3m.
10mm2 conductors would generally be adequate for 60A.
Reply to Pretty sure my cps assessor was wrong in the UK Electrical Forum area at ElectriciansForums.net
I am looking to join a CPS. I have looked at NIC Napit and Blue Flame. Just for a small cost difference Napit a Nic look to be a better option...
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
5K
I'm having a bit of a disaster at the minute and would like an honest opinion. I am having a gas stove fitted in the corner of my room and...
In addition to the 4 main, well known competent persons schemes (NICEIC, ELECSA, NAPIT and STROMA), there is apparently another, lesser known...
7K