EWell there is a clue.....

If its just the main fuse then don't you think there must be a problem betwixt fuse and....board!
 
IR test between poles on the DP switches.....check main earthing...see how much currents on it.....
 
also....hang around for a bit....see if the current draw suddenly jumps up....as if theres a "secret load" anyware..lol....
 
I would check the connections on the cutout/ryefield fuseholders that hold the 60a fuses that keep blowing.
If there is heat build up here due to loose terminations/fuse blades/contacts the heat could melt the fuse wire with only a few amps flowing.
By the time you return to site the fuseholder will have cooled down so you would never know.
 
A quick way to check for heat build up is the temperature sensing labels sold by RS. I’ve used them on fuses before. Will have a look for them later, busy cooking at the mo.
 
A quick way to check for heat build up is the temperature sensing labels sold by RS. I’ve used them on fuses before. Will have a look for them later, busy cooking at the mo.
your always bloody cooking Tony...lol...
 
A quick way to check for heat build up is the temperature sensing labels sold by RS. I’ve used them on fuses before. Will have a look for them later, busy cooking at the mo.

I bet it isn't Puy lentils in creme fraiche and white wine, salmon baked with lemon and garlic, new potatoes, 10 minute old asparagus and roast parsnips coated in butter???
 