Get your customer to speak to the supplier whilst you're there with them, it could just be a case of how the question was asked.
Yes I have a generic RA,but I’ll be honest the fairies always seem to beat me to the seals anyway......That might be because for every job you are supposed to do a risk assessment/method statement and as a scheme member that's what you are expected (in theory) be doing.

SSE told me,over the phone admittedly, that as long as you are registered with a scheme you can pull the fuse and let them know afterwards.....
Thanks for the replies guys. Think I best speak to them as advised.I do recall these policies & procedure were being reviewed by the Energy Networks Association, to have a common approach. But I wouldn't be holding my breath.
SSE does have policy for domestic single phase supplies, if you search for procedure for removal & replacement of company cut-out seals by electrical contractors.
After completion of your works, use their temporary seals, and give them the details, to re-seal. Course you should carry out a risk assessment of the condition of the cut-out (i.e. removing main fuse) before doing so, and wear appropriate PPE.