Get your customer to speak to the supplier whilst you're there with them, it could just be a case of how the question was asked.
 
SSE told me,over the phone admittedly, that as long as you are registered with a scheme you can pull the fuse and let them know afterwards.....

SSE does have policy for domestic single phase supplies, if you search for procedure for removal & replacement of company cut-out seals by electrical contractors.

After completion of your works, use their temporary seals, and give them the details, to re-seal. Course you should carry out a risk assessment of the condition of the cut-out (i.e. removing main fuse) before doing so, and wear appropriate PPE.
 
I do recall these policies & procedure were being reviewed by the Energy Networks Association, to have a common approach. But I wouldn't be holding my breath.
 
SSE does have policy for domestic single phase supplies, if you search for procedure for removal & replacement of company cut-out seals by electrical contractors.

After completion of your works, use their temporary seals, and give them the details, to re-seal. Course you should carry out a risk assessment of the condition of the cut-out (i.e. removing main fuse) before doing so, and wear appropriate PPE.

I've uploaded the relevant document as a PDF file.
 