I was having a discussion with my colleague regarding burying a swa directly along with a pvc earth cable.
As the earth is not an armoured does this need to be ducted for mechanical protection and if so is there a regulation in the BS 7681 for it?
 
Yes 16mm 6491X or bare 25mm
 
I didn't like buying any cable directly in the ground/soil including swa. Always preferred to put it in some ducting.
 
  • Like
Reactions: nicebutdim and DPG
543.1.1 refers you to 542.3.1, and the minimum CSAs in table 54.1
 
Agree with Midwest, although swa is suitable I never liked burying it either, would always opt for a duct.
 
  • Like
Reactions: nicebutdim
As above 16mm can be buried without additional protection

Silly reg thou as if 10mm needs protection from a fork or spade surely 16mm does as well
 
  • Like
Reactions: timhoward
Yes I’m definitely not a fan of burying any cable directly myself as it is never sanded or dusted the way it should to protect against sharp stones although the consultant has specified it this way. I know swa can be buried directly but I am unsure of the regulation for non armoured cables buried directly. Need regulation to let the consultant know.
 
Yes I’m definitely not a fan of burying any cable directly myself as it is never sanded or dusted the way it should to protect against sharp stones although the consultant has specified it this way. I know swa can be buried directly but I am unsure of the regulation for non armoured cables buried directly. Need regulation to let the consultant know.

P198 and 199 of the BBB (brown)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
PVC cables buried direct
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
FRPB84,
Last reply from
DPG,
Replies
7
Views
1,511

Advert