just a quick question. im installing 10 x 4 foot fluorescent fittings, each with 4 x 36w tubes.
I was under the impression that each fitting would use 144watts, so all 10 would be 1440watts, which would be 6.2 amps in total.
The problem is it keeps tripping a 10 amp breaker and when ive had a clamp meter on the cable it says its pulling 11 amps.
Theres no more lights on the circuit, am i calculating something wrong?
 
If you multiply your 6.2A by the 1.8 factor for discharge/fluorescent lighting you'll arrive at 11.1A.


Is the breaker tripping on startup or after a period of time??
 
The reason lenny was asking this was flourescent luminaires have ballasts on them which are inductives. This can cause a B type breaker to open.
 
it popping after about 5 mins. does the 1.8 factor just apply for the initial start up?

The 1440W figure is the real power but the apparent power (VA) is higher because there is a power factor associated with lamps because they are an inductive load. This is giving the 11A+ figure that you are seeing on your clamp meter. This will be there the whole time and cabling and volt drop should be calculated on the apparent power. As Lenny said multiplying watts by 1.8 is usually accurate enough. However your 10A mcb should not be unduly troubled by 11A for 5 mins so the tripping is probably down to a combination of the inrush / startup current and the overload. The peak inrush for the ballasts should be in the manufacturers specs. Inrush can be countered by using a C type breaker ( if the max Zs is ok) but that still doesn't solve your overload. I reckon you probs need 2 circuits both on 10A mcbs :)
 
Last edited by a moderator:
The 1440W figure is the real power but the apparent power (VA) is higher because there is a power factor associated with lamps because they are an inductive load. This is giving the 11A+ figure that you are seeing on your clamp meter. This will be there the whole time and cabling and volt drop should be calculated on the apparent power. As Lenny said multiplying watts by 1.8 is usually accurate enough. However your 10A mcb should not be unduly troubled by 11A for 5 mins so the tripping is probably down to a combination of the inrush / startup current and the overload. The peak inrush for the ballasts should be in the manufacturers specs. Inrush can be countered by using a C type breaker ( if the max Zs is ok) but that still doesn't solve your overload. I reckon you probs need 2 circuits both on 10A mcbs :)

Good answer mate.
 
one more thing, anyone know any good books regarding the design side?

If it is a case of you knew it once and have forgotten then the IET's electrical installation design guide is ok and it has some examples, but it does go into a lot of detail and you might find it heavy going. If you are more of a beginner then On Site Guide is a good a place to start as anywhere. (appendix F in the new one)
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined

Thread Information

Title
quick calc question
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
12
Unsolved
--

Advert

Thread statistics

Created
luke12345,
Last reply from
luke12345,
Replies
12
Views
1,433

Advert

Back
Top