B
Brightspark2
There's no need to be like that! How come is doesn't comply with regulations?
My previous house, I updated my consumer unit to a Split board with Dual RCD which everything in the house feed from a RCD covered circuit and i got that passed with no problem and it didn't cause tripping.
This is what i would do in the middle of the night. Pull out all fuses, Reset RCBO, Put each fuse back in one at a time, if it trips, leave out till morning and sort.
I'd like to add, i've already done an insulation resistance test, R1 +R2 test for all the circuits already. all are perfectly fine.
I wasnt being funny with you there squire, I'm a friendly member of the site. If the fault was N-E you can take the fuses out and it would still trip. Youd be stuck with no power. It doesnt comply with regulations. To be honest even a split load consumer unit is a compromise but it's done due to cost otherwise they would all be RCBOs.
As teletrix says you may not need the RCD protection.