Discuss rccb tripping (regularly with new oven) in the Industrial Electricians' Talk area at ElectriciansForums.net

S

salisbury spark

Customer had comet install a (12kw)standalone commercial cooker. RCCB trips 90% of the time when oven switched on (2kw oven)and also while oven operating. (hob is fine). Cable is 6mm on a 40amp mcb which needs sorting (should be 32a mcb on 6mm says BRegs) and should uprate to 10mm cable(due to load). But why is rccb tripping so much (40a mcb not tripping) either intermitent fault in oven or rccb to sensitive. Dont rate rccbs, prefer rcds. - Do you recommend trying a RCD or most likely a oven fault?- need help of an experienced electrician (cirrus r u out there)....all advice welcome.
 
Hi Sailsbury. Just to inform you I am not a qualified electrician yet but have been doing lots of revision on fault finding for my exams.

I have read quite a few articles about heating elements in ovens containing water when new which can cause earth leakage problems. I don't really know how to check this but have read that some electricians bypass the protection to run the oven for an hour or so to dry out the element.

If it is an earth leakage fault this could explain the mcb not tripping!!! Hope this helps.

Can anyone on here confirm this????
 
When i did my City and Guilds course, my tutor who had some 30 years + experience told us not to put an oven circuit on rcd, because of nuisance tripping, because of earth leakage from the elements in an oven, like Eskimo was saying.
However with the 17th edition updates, they say that ever new circuit installed now, should be protected by rcd. So im not sure where we stand with this now. Does the customer just have to bare the inconvenience of resetting their rcd every time it trips with the oven on ??
 
Customer had comet install a (12kw)standalone commercial cooker. RCCB trips 90% of the time when oven switched on (2kw oven)and also while oven operating. (hob is fine). Cable is 6mm on a 40amp mcb which needs sorting (should be 32a mcb on 6mm says BRegs) and should uprate to 10mm cable(due to load). But why is rccb tripping so much (40a mcb not tripping) either intermitent fault in oven or rccb to sensitive. Dont rate rccbs, prefer rcds. - Do you recommend trying a RCD or most likely a oven fault?- need help of an experienced electrician (cirrus r u out there)....all advice welcome.

Are we talking a 12kW or a 2kW oven? Its a big difference. :confused:
 
12kw total load including 2kw oven. - funny enough i told customer that new ovens will have moisture in them and will trip until dried out..... - Takes customer over 4hours to cook a simple meal in oven because of tripping. - Not really an acceptable excuse as ovens cook in moisture all the time... Customer skint at moment but will go back and another look thanks for everybodys input. TBC......
 

Reply to rccb tripping (regularly with new oven) in the Industrial Electricians' Talk area at ElectriciansForums.net

Similar Threads

Hi all, Was wondering if anyone has come across this before and could maybe help - Its a new one to me! Customer recently altered layout of...
Replies
7
Views
2K
Hi all just here as an enthusiastic learner/diyer to gain knowledge and help on bits and bobs At the moment I am confused I have a new single...
Replies
20
Views
3K
Hi, The current state of play is a standalone combined oven and hob supplied by single cooker circuit with 40A RCBO, 6mm cable, isolated by cooker...
Replies
1
Views
2K
Hi everyone. There is something that confuses me so I hope someone could answer. There is an electrical Hob which is 7.8KW and electrical oven...
Replies
14
Views
4K
Long time lurker so this may be my first question. I am a qualified electrical engineer, but in aeronautics not domestic installations, and I may...
Replies
21
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock