I have looked at a job today which is a shower install. trouble is it;s the old wylex box with rewirables in. there is a spare way and thought of using this to supply a small enclosure with RCBO unit in. can I do this without upgrading the tails etc. (bonding is in order)
The way I read it in the books is things have to comply to the current regs so uphrading required but hoping feeing it from existing slot gets away from this.

there was a shower in at some point which has been removed and it's fuse used for a cooker.

the property is a flat and the run for the tails will be a night mare......

any advice appreciated, Ross.
 
Making sure your new circuit complies would be fine, You have already checked earthing and bonding.
 
2 things to consider :

-Is the main switch capable of coping with the additional load /
-What rating is the shower ? & will your rewireable be able to supply it ?
 
You say you dont want to upgrade the tails......what are they now then????

Are you not able to break into the tails and supply a small CU just for the shower???
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
RCD fed via bs3036 (rewirable fuse)
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Ross Trician,
Last reply from
Guest123,
Replies
4
Views
2,905

Advert

Back
Top