Hello David.

The RCD is there for the protection of personnel who may inadvertently come into contact with live a.c. mains. This will not happen on a sub-distribution cable, so no RCD is required for this. The cable itself requires protection from short circuit conditions, and this is what an MCB does. A correctly-rated MCB will be required at the supply end. If personnel protection is deemed necessary for the final sub circuits, this should be provided at the remote end of the supply cable. Nuisance trips become an issue if this is installed at the supply end. If anyone sticks a drill or similar into the cable, the MCB will oprerate and disconnect it.

Regards,

Colin Jenkins.

I am also shocked by this advice. (No pun intended either)
Poor advice is more dangerous than none at all.
 
Last edited by a moderator:
Hello David.

The RCD is there for the protection of personnel who may inadvertently come into contact with live a.c. mains. This will not happen on a sub-distribution cable, so no RCD is required for this. The cable itself requires protection from short circuit conditions, and this is what an MCB does. A correctly-rated MCB will be required at the supply end. If personnel protection is deemed necessary for the final sub circuits, this should be provided at the remote end of the supply cable. Nuisance trips become an issue if this is installed at the supply end. If anyone sticks a drill or similar into the cable, the MCB will oprerate and disconnect it.

Regards,

Colin Jenkins.

This was why RCBOS /RCDs have to installed on all circuits that are not mechanically protected or deeper than 50mm within fabric of building now because apparently some MPs wife put up a metal spice rack with the fixing screw hitting the live conductor and making the spice rack live. The screw missed the earth so did not trip the MCB
 
Hello David.

With apologies, please ignore my earlier response - it's total rubbish.

As stated above, if the twe cable is hidden within the building fabric at less than 50mm depth and it is not mechabnically protected, then an RCD will be required at the supply end for personnel protection. Please note that a conventional 30mA/40mSec max. RCD should be selected for this; a time-delayed unit will not meet the requirements. The current carrying capacity of the RCD should match or exceed the rating of the selected mcb.

63 amps for the mcb sounds about right, but you will need to do the cable selection calculations accounting for Ze, the installation method and the total circuit length to confirm this.

Regards,

Colin Jenkins.
 
Hat off to you Colin for holding your hands up and expressing your original post was 'total rubbish', many members on here would just go into hiding when they mess up..... having said that im a little worried that amongst all the members that made such a basic error it was a consultant of many yrs experience as i struggle to see this error was made due to misinterpretation of the OP as he was clear regarding the run of the cable....

We all make boo boo's though even me and at least you took this one on the chin! :smartass2:
 
Hello Darkwood.

Thank you for your note and your thoughts. This forum is for all of us to make our best efforts to assist others; if an unintentional goof-up gets in the community promptly and politely corrects it, as has happened here. My first response was framed in industrial-think (where I spend most of my time). A "steel conduit and SWA" world, although the OP clearly stated he was installing TWE!

Once again, I apologise for the hassle my reply caused and have gone to the Dunce's Corner for a while.

Regards,

Colin Jenkins.
 
Hello Darkwood.

Thank you for your note and your thoughts. This forum is for all of us to make our best efforts to assist others; if an unintentional goof-up gets in the community promptly and politely corrects it, as has happened here. My first response was framed in industrial-think (where I spend most of my time). A "steel conduit and SWA" world, although the OP clearly stated he was installing TWE!

Once again, I apologise for the hassle my reply caused and have gone to the Dunce's Corner for a while.

Regards,

Colin Jenkins.

Nice to hear Colin. Compared to "other" electrical forums, this one usually gives out excellent advice, and I'm glad to hear that you're big-enough to hold your hands up when you realise you goofed up. :)
 
Hi guys the T&E was installed before I quoted the job so swa is not an option.

It does need RCD protection because its being installed in a dot and dab wall.

I am fitting a dual RCD board to 17th edition

But want to protect the submain with a time delay RCD to avoid nuisance tripping?

All circuit will be protected by 30ma RCD but the submain will be on a time delay RCD to avoid conflict between the two Rcds.

I have always installed a 30ma RCD on the submains but when a fault happens writhing the property it can take out the RCD front end which means a long walk to re set?

Hope that makes sense

The earthing system is tncs (not sure why that matters to this)
 
If the submain is T+E and installed less than 50mm in a wall then it will need additional protection by way of a 30mA RCD. A Type-S is not suitable for the provision of additional protection.
 
Ideally, the submain would be SWA so you wouldn't have to. Two RCDs inline is usless because you can't discriminate. Is there any way for you to be able to protect the T+E with an earthed metallic plate?
 
Deleted OP whipped my butt then i realised i mixed this thread up with another Oopps!:bucktooth:
 
Last edited by a moderator:
Yea I could get round that.

It's just my old boss use to use time delay RCDs all the time to stop nuisance tripping

When he did a periodic report he would list two 30ma RCDs inline.

On an existing insulation with cables installed is there Any way of protecting the consumer unit and submain without discrimination?

Where should a time delay RCD be installed then?
 
Time delayed RCDs can be used to protect submains to achieve a specific disconnection time allowing for discrimination with other RCDs further on in the circuit. They cannot be used for additional protection, only 30mA RCDs and supplementary bonding can be used for additional protection.

If you can protect the T+E with an earthed metallic plate at least 5mm thick then do that, if you can't, you either put up with having the whole submain on one RCD or rip out the T+E and replace with SWA or similar.
 
Dark wood i find you a bit rude and insulting.

I have not installed the submain

The will be not be exporting the earth as it it's a granny flat connected to the existing house. Basically a big extension?

My old boss used a time delay RCD and I was just after more information on this method as I've never done it myself. (Obviously he was not doing it correctly)

I came on here for a bit of friendly advice that's all. In future I think I will not ask questions to improve my knowledge and try to keep learning just incase I get this sort of response

Thanks for putting me off this site
 
Apologies David i actually mixed your query up with another thread!


I suggest you throw away your teachings from your old boss as it sounds like his --- and elbow must have looked very similar to himself, the supply cable while it stays as is requires rcd protection 30mA - No time delay

Take the board out and fit a standard board mainswitch with mcb set up's or replace the submain supply with a mechanically protected cable like swa.
 