Lets clear this up a bit ......

Rcd's in parallel - general rules.

Putting RCD's in series would give discrimination issues
As the circuit is a distribution circuit reg' 411.3.2.3 allows a disconnection time of 5s
As the dist' circuit is exceeding 32A reg 411.3.2.2 means it dosn't have to trip in 0.4s
Given the above you CAN have 2 rcd's in series if the distribution circuit rcd is time delayed as a time delayed rcd will trip in <5s.

This still wont achieve discrimination though as a N-E fault would still trip both rcd's so to prevent this you can ensure all downstream devices requiring rcd protection after the distribution circuit are protected by a rcd that breaks BOTH live and neutral. reg 531.2.9

So yes you can have 2 in series as above and comply but you need to confirm that the 17th edition board has double pole rcd's as most do if you are fitting a board with rcbos anywhere in it even fitting rcbo's within the unprotected ways of the 17th edition board then you will have issues as these are not double pole and you wont achieve discrimination.

In the design stage just having an swa to start with saves alot of time and can be cost effective believe it or not after all the supplementary earthing with the sub-main or time wasted trying to ensure the earthing in the t&e is sufficient.

Additional edit ....as had breakdown and didnt have time to look it up...

Your set-up with cable <50mm and no mechanical protection!

Now for the technical bit ;)........ Reg 522.6.7 species that if all points of reg 522.6.6 are not met in this case a t&e less than 50mm below surface without mech' protection then RCD protection is required-- so far straight forward then it refers to the characteristics of the rcd must comply with reg 415.1.1. which specifies that the rcd must not exceed 30mA and an operating time not exceeding 40ms at a residual current x5.

Thus we now refer to appendix 3.... now this is where as pointed out earlier you confuse us... time delay rcd's start from rating 100mA but looking at the table and assuming you can purchase a 30mA rated S-type it shouldn't effect the trip times against other ratings of S-Type, if you look in the X5 column the tripping characteristics clearly show S-types trip between 40 and 150ms which would mean your install would contravene regulation 415.1.1 because you are using rcd to provide additional protection so it must trip within 40ms at x5 which cannot be done with a time delayed rcd so a standard rcd must be fitted and then we are back to square 1 as you dont have discrimination of rcd's.

Solution ...Swa or othe mechanically protected set-up.

Its ok that your old boss was laying down the rules to you but he also needs to learn his job he's used a set of regulations to show compliance but ignored others that have priority on the situe..... hopefully after all my input here we cn lay this to rest that you can't have in your design a time delay rcd covering the sub-main because it is required for additional protection so must be a standard rcd 30mA with no delay.
 
Last edited:
apologies if this has been suggested before. i've not read all the posts. from what i gather, it's the T/E installed in the dot&dab wall that's the problem. ( 522.6.101). this could be overcome by enclosing the T/E in earthed steel conduit for the relevant part of the cable , thus negating the need for a RCD upstream.
 
POST 61.... this is how i interpret the regulations in the OP's case regarding having a time delayed rcd on the sub mains to try achieve discrimination .... feel free to pick at it as you will as we all know the reg's aint always straight forward and can be interpreted in differing ways...
 

Reply to Rcd- mcb in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
I have a 40amp RCD downstream of a 50a MCB (10mm csa cable) should the MCB be lowered to protect the RCD from overload? If so why does this not...
Replies
4
Views
785
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
943
Hi there , Currently doing a college project where i need to select protective devices for the contract. I'm now at the point of selecting SPDs...
Replies
5
Views
2K
Doing a kitchen job for my daughter’s music teacher, who also happens to have been in my wife’s class at school. Nothing big… just a little...
Replies
2
Views
269

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock