This is the info we lacked when you progressed through your thread and we have to assume by what you post ....hence a few of us brought up the exporting earth ...if it was a garage several meters away and of a exposed steel contruct then this would be a possible situation for TT-ing the garage. We now know this is all irrelevant as its not the case... but i think you are now clear with where your issues lie regarding needing to protect the submains with both overload and 30mA rcd protection.
Yes your in a corner if the rcd trips then to the garage it is.... only way around it is to mechanically protect the existing sub supply or replace the existing with SWA.... you have your options now put your argument forward for replacing the sub mains cable.
You could just have the set up as is with 63amp mcb and 30mA submain protection on the 17th edition board and yes poor design and not professional to leave as such but if not your design just argue your corner and do within reason what they ask.
Yes your in a corner if the rcd trips then to the garage it is.... only way around it is to mechanically protect the existing sub supply or replace the existing with SWA.... you have your options now put your argument forward for replacing the sub mains cable.
You could just have the set up as is with 63amp mcb and 30mA submain protection on the 17th edition board and yes poor design and not professional to leave as such but if not your design just argue your corner and do within reason what they ask.