if its tripping in the correct times then theres nothing to worrie about, however RCDs should trip whe you cut through the cable even if its dead because its detecting a dead short between live and neutral

Really, please do as Tony says...
 
If you cut the wire after a double pole fused spur the only cable connected back to the fuse board is the earth, therefore no fault will be seen by the RCD

Edit: Sorry , Sedgy34 beat me to it
 
What did the rest if your testing show? Were the results what you expected them to be? What was the earthing arrangment out of interest?

Rich
 
Its a little disapointing to hear some silly responses in this thread

Especially since its not as if rcds and why and how they operate takes a rocket scientist to understand
 
i think people get mixed up with "if the circuit is dead" and "if the RCD is dead"....if the circuit is dead..but the RCD is still energised....then it will still sense a N-E fault on the dead circuit.....but if the RCD is dead....then of course it wont sense any faults on the circuit/s it feeds.....
 
i think people get mixed up with "if the circuit is dead" and "if the RCD is dead"....if the circuit is dead..but the RCD is still energised....then it will still sense a N-E fault on the dead circuit.....but if the RCD is dead....then of course it wont sense any faults on the circuit/s it feeds.....
Is it a faulty rcd then if so why would the tester still give good tripping times
 