Hi looking a little help. Replaced a consumer unit in a house with a contactum 8way dual rcd split board. After finishing it I tested with rcd tester at 1 time and 5 times with the rcd tripping in correct times. I went to connect up boiler after with the cable dead I cut it but the rcd would not trip. Then at the db I linked out the earth bar and neutral bar and neither rcd tripped to try and see if it would anyone any ideas?
 
if its tripping in the correct times then theres nothing to worrie about, however RCDs should trip whe you cut through the cable even if its dead because its detecting a dead short between live and neutral
 
Hi looking a little help. Replaced a consumer unit in a house with a contactum 8way dual rcd split board. After finishing it I tested with rcd tester at 1 time and 5 times with the rcd tripping in correct times. I went to connect up boiler after with the cable dead I cut it but the rcd would not trip. Then at the db I linked out the earth bar and neutral bar and neither rcd tripped to try and see if it would anyone any ideas?

your spur for the boiler is double pole so when you cut it it didnt register through the rcd
 
If you cut the wire after a double pole fused spur the only cable connected back to the fuse board is the earth, therefore no fault will be seen by the RCD

Edit: Sorry , Sedgy34 beat me to it
 
i think people get mixed up with "if the circuit is dead" and "if the RCD is dead"....if the circuit is dead..but the RCD is still energised....then it will still sense a N-E fault on the dead circuit.....but if the RCD is dead....then of course it wont sense any faults on the circuit/s it feeds.....
 
i think people get mixed up with "if the circuit is dead" and "if the RCD is dead"....if the circuit is dead..but the RCD is still energised....then it will still sense a N-E fault on the dead circuit.....but if the RCD is dead....then of course it wont sense any faults on the circuit/s it feeds.....
Is it a faulty rcd then if so why would the tester still give good tripping times
 

Reply to Rcd not triping in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock