Hi looking a little help. Replaced a consumer unit in a house with a contactum 8way dual rcd split board. After finishing it I tested with rcd tester at 1 time and 5 times with the rcd tripping in correct times. I went to connect up boiler after with the cable dead I cut it but the rcd would not trip. Then at the db I linked out the earth bar and neutral bar and neither rcd tripped to try and see if it would anyone any ideas?
 
Hold an RCD or RCBO in your hand with nothing connected, flip it to on and press test, report back
 
if its tripping in the correct times then theres nothing to worrie about, however RCDs should trip whe you cut through the cable even if its dead because its detecting a dead short between live and neutral
 
if you isolate a circuit using the MCB then cut through the cable, the RCD covering the circuits should (will) trip if the rcd is working.
 
if its tripping in the correct times then theres nothing to worrie about, however RCDs should trip whe you cut through the cable even if its dead because its detecting a dead short between live and neutral

It's time you did some reading!
 
Hi looking a little help. Replaced a consumer unit in a house with a contactum 8way dual rcd split board. After finishing it I tested with rcd tester at 1 time and 5 times with the rcd tripping in correct times. I went to connect up boiler after with the cable dead I cut it but the rcd would not trip. Then at the db I linked out the earth bar and neutral bar and neither rcd tripped to try and see if it would anyone any ideas?

your spur for the boiler is double pole so when you cut it it didnt register through the rcd
 