I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and with some misgivings I agreed to use it.
It came to testing.

Zs@DB of 0.3 ohms in garden room.
CPN RCD main switch tripped x1 at 21ms
The lighting circuit on a B6 had infinite IR values.

Semi-interestingly, a 'no-trip' Loop test at the light tripped the B6 breaker (and not the RCD). Both a Megger and a Metrel tester did this.
I got a measured Zs by shorting R1 and R2 at the fitting and testing bus bar to outgoing live at the CU. (0.40 ohms.)

I'm musing whether the MCB is just unusually twitchy, or it's actually faulty. Or maybe they all do it - I'm not used to CPN gear!
Any thoughts?
 
Last edited:
I see quite a lot of CPN gear in site cabins. Generally never encounter any issues, except one occasion when two RCBOs were faulty and wouldn't hold.
 
  • Like
Reactions: timhoward
I've never come across this fault, but a faulty breaker seems most likely to me
 
  • Like
  • Thanks
Reactions: DPG and timhoward

Similar threads

C
Replies
7
Views
883
E

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

timhoward

Broke Internet
Esteemed
Arms
Supporter
~
Joined
Location
Oswestry

Thread Information

Title
MCB trip (not RCD) during loop test
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
2

Advert

Thread statistics

Created
timhoward,
Last reply from
Pretty Mouth,
Replies
2
Views
1,443

Advert