On a job at the moment and office sockets have no RCD protection. They are ran in singles, PVC conduit. I am adding onto the circuit as additional rooms are in the process of being built. Do I need to protect the whole circuit with an RCD or can I just protect the new sockets with an RCD FCU? Whats the score with three phase boards and RCD protection? Do I need to fit an RCBO?
 
Last edited by a moderator:
if sockets are under the supervision of a "skilled or instructed" person, then there is no requirement in BS7671 to fit RCD protection.
 
No skilled people. Just offices workers and a store room. Best way to RCD protect sockets? RCBO?
 
any IT equipment on them?
 
No skilled people. Just offices workers and a store room. Best way to RCD protect sockets? RCBO?

Under the EAWR not only employers but employees are expected to know the dangers of electricity in the workplace and so I would say the office workers should come into at least the instructed persons category, as they should be instructed by the EAWR regulations and their employer
 
Last edited by a moderator:
In my experience of office fit outs etc working for several companies it has always been fine to not put on an RCD as the office staff etc are deemed instructed, as far as I remember this was something to do with the offices H&S that no staff should be touching anything electrical. Dont know how this would apply to smaller companies offices etc without strict H&S in place.

Could always fit an RCBO to be on the safe side, I probably would tbh. Then your covered either way.
 
Wouldnt bother with the RCD tbh then. Imagine the phone calls you would get when the IT server goes down because of nuisance tripping :-0
 
Going to put IT sockets on non RCD radial.... I need an earth going back to the board?? Then going to have seperate Circuit for other socket outlets for cleaners and hand tools in store room on rcbo?
 
for the IT sockets, a radial is fine, but you need to install hi integrity earthing.
 
Not too sure where to go on this one....? What reg lets you get away with not RCD protecting sockets...other than the 50mm rule and also the under skilled occupation....Because I don't consider regular office staff as "skilled" Electrically..... I also though do not want a case of nuissance tripping.....Whats the best way to go in your honest opinions?
 
you only need 1 "skilled" person ( manager ) in the office. all other staff can be "instructed" persons. i.e they are instructed by the skilled person not to mess about with electrical equipment.
 
So would this be noted on the EIC...."Under supervision of skilled person". Can you give the manager "skilled" status though?
 
On a job at the moment and office sockets have no RCD protection. They are ran in singles, PVC conduit. I am adding onto the circuit as additional rooms are in the process of being built. Do I need to protect the whole circuit with an RCD or can I just protect the new sockets with an RCD FCU? Whats the score with three phase boards and RCD protection? Do I need to fit an RCBO?

Are the conduits running surface or chased into the walls?
If everything is surface then no RCD's are require
 
no reason why not. not all managers are numpties despite what we call them.
 