What about through ceiling spaces though? They are going to be dropped into PVC conduit from a ceiling space.Are the conduits running surface or chased into the walls?If everything is surface then no RCD's are require
What about through ceiling spaces though? They are going to be dropped into PVC conduit from a ceiling space.Are the conduits running surface or chased into the walls?If everything is surface then no RCD's are require
Going to put IT sockets on non RCD radial.... I need an earth going back to the board?? Then going to have seperate Circuit for other socket outlets for cleaners and hand tools in store room on rcbo?
no reason why not. not all managers are numpties despite what we call them.

I need an earth going back to the board??
for the IT sockets, a radial is fine, but you need to install hi integrity earthing.
I know this is an old thread, but do you always install a high integrity earth to circuits supplying computers or do you check to see if there is 10mA to the cpc on that circuit first?
Also sockets on the same pillar that don't have PC's plug in would you consider RCD sockets?
I only ask because being a newer to the party than some here, I wouldnt trust employees to be considered instructed under the EAWR regs