I had a new 100mA S type on a distribution circuit that would trip before a 30mA on the final circuits when a HF fluorescent was turned on. Turned out to be a faulty 100mA RCD which was tripped by interference, a replacement from the same manufacturer had no problem.
 
It was explained in the link i give you .... if you find it hard to grasp dont worry learn to walk before you run..... the imbalance isn't a measured one you have on the load side ... its like a biased created normally on the L - E from effects like capacitance due to the PD been 230v where the same capacitance is present on the N side with little or no PD to earth the effect is small so you get a generated imbalance that the RCD core see's before you even consider your own leakage of your loads.... and i dont think you can measure it either it can be created by heavy loads switching in adjacent properties etc ....not easy to understand but as i said dont worry i doubt you'll ever see this issue due to these causes again.
 