You could find the offending circuit by removing neutrals but it would only indicate which circuit if the fault was there continuously

I will stick my head on the line here and suggest your fridge is causing the tripping when its compressor is switched into use

If you were to run this suspect appliance(or any other for that matter) from a socket fed by the other Rcd (using an extension lead) and see if you can get an appliance to cause the other Rcd to trip.it will be a process of elimination but you should get there
Does this Rcd also supply a light circuit with a outside light perhaps

Agree with Des, that fridge is the first thing I'd rule out, before trying anything else.

Nice track by the way Pete :cool:
 
A bit of a drastic action to resolve a fault.
the idea behind the post was that it would not only solve his electrical problem, it would also fix the many issues of a new build, e.g. dry lining, weetabix floors, unseasoned timber, wonky roof trusses that bar access to attics,, 3 tons of insulation, studded walls, and all the other cheap and nasty practices that came in on the 1960's and 1970's, along with mowtown, and rapp "music".
 
the idea behind the post was that it would not only solve his electrical problem, it would also fix the many issues of a new build, e.g. dry lining, weetabix floors, unseasoned timber, wonky roof trusses that bar access to attics,, 3 tons of insulation, studded walls, and all the other cheap and nasty practices that came in on the 1960's and 1970's, along with mowtown, and rapp "music".
If you think they were bad then you should see some of the new builds done now !.
 
QUOTE - [ They have been off every time RCD trips.

If power goes to the light fitting and then via a switch loop,
then moisture can still get in and cause problems even when the switch is off !
 
Can't believe some of the responses I've read to this.

The MCBs aren't tripping because it's an earth leakage fault not a current overload fault.
The fault isn't definitively a N-E RI fault but could still be a L-E RI fault.
The ONLY way to find out is to use an insulation resistance tester on each of the circuits to find the one with low IR, then remove all connected devices from that circuit (you may have double pole sockets but how can you be certain they are all DP sockets?, one may have been replaced/fitted with SP).
Do a continuity test between live and neutral to prove all devices are disconnected.
Then test the circuit again, if you've still got a low IR the fault is in the fixed wiring/accessories. If the IR reading is OK then it was one of the connected devices. Use the IR tester on each to find out which one.
 
Can't believe some of the responses I've read to this.

The MCBs aren't tripping because it's an earth leakage fault not a current overload fault.
The fault isn't definitively a N-E RI fault but could still be a L-E RI fault.
The ONLY way to find out is to use an insulation resistance tester on each of the circuits to find the one with low IR, then remove all connected devices from that circuit (you may have double pole sockets but how can you be certain they are all DP sockets?, one may have been replaced/fitted with SP).
Do a continuity test between live and neutral to prove all devices are disconnected.
Then test the circuit again, if you've still got a low IR the fault is in the fixed wiring/accessories. If the IR reading is OK then it was one of the connected devices. Use the IR tester on each to find out which one.
Right RI fault?
 
Can't believe some of the responses I've read to this.

It could simply be accumulated earth leakage from a variety of sources of equipment on the circuit(s) - you will not find this out simply by doing IR tests.......... you need a clamp meter..................................

Seen this on a number of occasions.........
 
It could simply be accumulated earth leakage from a variety of sources of equipment on the circuit(s) - you will not find this out simply by doing IR tests.......... you need a clamp meter..................................

Seen this on a number of occasions.........
Preferably one that reads miliamps
 
I'm with Tel on this. New builds are generally built like an Ikea wardrobe, no solid backbone, no integrity, just done to the lowest common denominator. The fact that we as a society have taken generations to master all aspects of building, and then accepted the carp that is produced is woeful. Yes, economics (and greed) play a part, but the standards we currently accept are sad.

So, get it knocked down and build a proper house!! Or move....

Re the OP; Murdochs suggestions sound a good plan to me.
 
Unfortunately, the lottery numbers haven't come through yet so moving will have to wait until this weeks Euromillions draw.

In the mean time - Ok here it goes, I'll wait for the onslaught. "Would it help (if room in the CU) to replace the MCB's with RCBO's, to determine the circuit that may be causing the issue".
 
Shouldn't be necessary. Apart from the cost, the risk is a second fault may be introduced doing the change. I prefer to fix known faults first :)
 