Murdoch,

I agree that it sounds very odd which is why I wanted to get some views on here, I have done a fair bit of fault finding but never had this scenario.

When you had split the ring, with both halves disconnected at the cu, did you check for continuity between them as it sounds like there is an interconnection
 
Everything is unplugged.

Assegayer, that was my next thought also, I just cant understand how it has a fault on both sides
 
Either two faults, or, there is another interconnection in the ring (ie wired up like an "8", not a "0").

Edit: oops, too slow! :)
 
Last edited:
A lot of work is being done in the house, a new boiler a month ago and new kitchen recently, they say nothing was being done when it tripped off.
 
It is generally vey poorly wired, none of the cpc's behind the sockets I looked at had any sleeving.
 
Last edited by a moderator:
yep as murdoch said, then just take it nice and easily, me personally I like to just do old fashion and bell things out and then label so i know which things are where and then you can track the fault relitavely quickly and i just use the rcd as the main tester lol keep splitting and checking if its okay best way IMO
 
Well I had another look and I have seen nothing like it. I disconnected one of the sockets about mid way and checked the resistance of r1 on both sides of the ring, and both sides gave approx 0.51 ohm, I then disconnected other sockets and on a 13 socket circuit only three made a difference to the reading, a couple gave open circuit on both sides. Customer has decided that they want it all redone correctly as a ring as every job in the house has been done wrong and installed by the DIY previous owner who had no clue.
 