One of my electricains on site has just called me with a very strange problem. We have installed a 18 way split load board into a domestic dwelling as normal, he tells me that if he turns all of the breakers on that are on the RCD side the RCD trips, but if he leaves 1 of them off it does not trip? my first thought was that the circuit he turns on last has a fault but he assures me if he turns this on on first and leaves another off its ok. I am 100% sure its not over loaded, please advise.
Many Thanks:confused:
 
Dual RCD CU?

Sounds to me like he has the neutrals for each RCD swapped over and connected to the wrong bars.
 
This kind of fault where RCD's are tripping randomly are generally down to installer error as i explained above.

It could be a circuit neutral in the wrong place also.

Maybe get your electrician to check and double, double check.


I do this more often than i care to admit.:)
 
Has he tested all of the circuits? Could be a neutral to earth fault, or a faulty appliance. Had many leaky fridges/freezers, also vaccuums(is that how you spell it!).
 
Cheers guys, I have visited site and changed the RCD! seems to have been a fault on that. One of those one where you try everything and the last thing to check it is.

:)
 