Oh for god sake. I thought this forum was to clarify doubts people have. Ya give the advice and either ya get shot down or the op gets told he don't know what he is doing. Surely this is why a forum exists and not for just showing you know more than someone else.
To clarify... Put the 40a type 1 mcb in the board only and run to the RCD. DO NOT put a 40a in the board and then another one in with the rcd unit. This will cause a discrimination issue.
this attitude is exactly what is wrong with this forum. The op clearly needs more than clarification, the don't know the basics yet you are willingly handing out all the answers. In my opinion that is foolish. I thought it was an "electricians" forum. People that need basic questions answered are NOT electricians