baldsparkies
Just popped home for a cuppa, anyway sounds like your only problem is with functional testing of the RCD all else is ok. (Is that right)
If so I would follow the advice of previous posts regarding changing the RCD again. As said, its not immpossible for the new unit to be faulty.
Remember the test button generates an inbalance through the coil using a line resistor, that generates an eddie current in the relays secondary winding and the generated voltage differance operates the relay, with this in mind have you checked the mains voltage under load ? Also dont forget to check your tripping times on both ends of the waveform ie 0 degrees and 180.
It doesn't sound like a low neutral to earth resistance otherwise the rcd would be nuisance tripping, or crossed neutrals at the neutral bar. That would cause tripping the moment the offending circuits were energised.
Hope this info helps
If so I would follow the advice of previous posts regarding changing the RCD again. As said, its not immpossible for the new unit to be faulty.
Remember the test button generates an inbalance through the coil using a line resistor, that generates an eddie current in the relays secondary winding and the generated voltage differance operates the relay, with this in mind have you checked the mains voltage under load ? Also dont forget to check your tripping times on both ends of the waveform ie 0 degrees and 180.