Discuss rcd's retrospective on socket circuits in the Canada area at ElectriciansForums.net
S
sutt777777
can anyone clarify if rcd protection is required retrospectively on ring main/socket circuits in industrial premises.
I have been given a job to clear up snags on a periodic inspection, the lack of rcd protection is given as a failure on a number of circuits.
it's not a problem, i would replace a number of DB with new ones with prob rcbo's to avoid nuisance tripping.
Just don't want to charge customer if not required.
Cant find the reg in the book with regards to retrospectivity
any help much appreciated
Hi my view is that if its a pir pre 17th which it must be, any socket outlet capable of supplying equipment for use outside should be rcd protected.This is regardless of installation.The 17th edition is more strict with the use of rcds.It maybe possible just to protect a circuit rather than change a board.
Reply to rcd's retrospective on socket circuits in the Canada area at ElectriciansForums.net
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Evening all, If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or...
6K
Hi All Hope someone can help In industrial setting are all circuits required to be RCD protected ? Or is it just socket circuits ? Thanks in...
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
6K
Haven't been on here for a while, so sorry if this has been discussed before. BS7671 2018 + A2 Regulation 421.1.7 recommends AFDDs for...
9K