hey, i was rung today by my dad to come and look at a glasswasher that is causing the main RCD incomer to trip every time it trys to cycle.
This glasswasher is in a pub, over the last 2 days the landlady said every time she tried to cycle the dishwasher it tripped all her pumps out. The glass washer powers up fine and fills with water everytime it tried to run a cycle tho it tripped the RCD on the fuseboard, its a really old fuse board didnt catch the name but im going bk tomorrow after work to investigate more. my thoughts was could it be the element that is nakard and causing this tripping? if not any ideas?

also the shower in the flat above the pub is causing tripping aswell. The fuseboard in the flat is a dual RCD split board, the shower switch has recently been changed and so has the shower as the last 1 was nakard. now this is the interesting part. when the shower switch is turned on it powers the shower no problem, then when you push the power button on the shower it causes the opposite rcd to trip not the 1 feeding the shower side. Ive not had any experience with split rcd boards being in the commercial side of things. and this 1 is baffling me a touch. now i havnt had the cover of the board off to see whats going on inside ill be doing that tomorrow on my return visit. i just thought id post on here to see if any of you have had similar situations of this. also to maybe save myself some time when going back tomorrow. i dont have full test equipment available either this is a favor for some1 so just trying to help out without it costing them a fortune.

is it a coincidence these are tripping together or could it be something further down the line?
 
you could wel, be right on the dishwasher. as for the shower, check that the neutral is in the correct neutral bar in the CU. and you really need an IR tester to proceed any further.

edit. paul.m is close to you if you get stuck.
 
Last edited:
that was my thoughts on the neutral but will have to check tomorrow. The board hasnt been installed too long and i know of the company that installed it, ill see what tomorrow brings though just after some possible pointers before i waste loads of time
 
What good would that do in a split board??

It would mean that only the shower would trip, and not half the circuits in the house.

To the OP, if you haven't taken the cover off then you can't be sure the shower is on that side. It won't be the first time someone has moved a circuit from one side to the other and not updated the schedule on the front of the board! Or is it obvious by the MCB size where the shower is?
 
Surely with a split load board, you would expect there to be a load almost constantly on each side of the board, with each side being monitored by a separate RCD. So if the N for the shower is put in the wrong side, then side A (with the shower MCB) would have less neutral current than Line current and side B would have more Neutral current than Line current. I thought RCDs detect an imbalance, regardless of whether it is the Line or Neutral has more current flowing than the other. If they only detect when there is less Neutral current than Line current (because the shower N is in the wrong side), then I would expect the shower side to trip, not the other one.

Or is this a split load board with RCD on one side only? Shower MCB on non-RCD side?
 
It would mean that only the shower would trip, and not half the circuits in the house.

Wouldn't really tho would it, if both rated at30mA it would be pot luck which one went out first


Even if the other side pops and the shower keeps running, then the shower side will exhibit a difference in current between L and N on that side, and should therefore trip as well.
 
Last edited:
edit. paul.m is close to you if you get stuck.


"He's off to have a look at it after work" and "its in a pub." Count me in but your driving :).

I'll pm you my number if you need a hand.

First place to look at is that new switch, it worked ok before that was changed? Next step the cu, visual first then an IR test as above, if that's not the problem then clamp meter cpc at the cu as it could be accumulated earth leakage.

You say it trips when the shower on/off button is pushed. Let's have a look at the element, probably the same problem as the dishwasher in the pub.
 

Reply to RCDs tripping in the Australia area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
996
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock