bigspark17

-
Arms
Reaction score
718
Should main switch on tncs isolate all poles.? Switch in the pic only isolates the three phase conductors!
Reg no?

IMG_1333.JPG
 
There is no requirement to isolate the neutral in TN systems as far as I know except for domestic situations where the switch is intended for use by householders.
 
Andy correct as always :)
537.2.1.1 - says for TNS and TNCS its not required to sw neutral
537.2.1.7 - provision of a way to ISO neutral must be provided (a link)
537.1.4 - single phase domestic both L & N to be sw.
 
I looked for ages at this picture for the main switch Bigspark. Then I saw you pointing at it. :):)

I think he's actually pointing at the sticker posted by the NICEIC contractor that appears to state an installation date of June 2014 and recommends the next test date as June 2014. Maybe not very confident in their work ....... lol.
 
I think he's actually pointing at the sticker posted by the NICEIC contractor that appears to state an installation date of June 2014 and recommends the next test date as June 2014. Maybe not very confident in their work ....... lol.
A least they're not responsible if something goes wrong a couple of days after testing Andy.
Past its retest date.
 

Reply to Reg no for main switch on tnc-s in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, if I cannot access the line side of a crabtree 100A DP main switch. Would someone enlighten me how to conduct safe isolation on this...
Replies
15
Views
1K
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
821
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
442
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
First, sorry if I'm not in the correxct thread. I'm trying to replace an old switch with a WIFI switch and cannot seem to do it right. There are...
Replies
1
Views
313

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock