For disconection times we have to hit 0.4 for up to 230v U0. 0.2 for 400-1000U0.

I always took this to mean what it says.

both single and 3 phase V to earth is 230, so we use the 0.4 disconection.


Taking my 17th update and got told that was a typo!!!!

So for 3 phase we are supposed to use 0.2, single 0.4.

Now that is not what the book says!

So what am I supposed to design my circuits for?!

The question is partially moot as I always use MCBs so they knock off in 0.1, but that is not not the point.

When I chuck in my next 88, what should I desgin it too?
 
For disconection times we have to hit 0.4 for up to 230v U0. 0.2 for 400-1000U0.

I always took this to mean what it says.

both single and 3 phase V to earth is 230, so we use the 0.4 disconection.


Taking my 17th update and got told that was a typo!!!!

So for 3 phase we are supposed to use 0.2, single 0.4.

Now that is not what the book says!

So what am I supposed to design my circuits for?!

The question is partially moot as I always use MCBs so they knock off in 0.1, but that is not not the point.

When I chuck in my next 88, what should I desgin it too?

There is no 'typo' it's 0.4 seconds and it is Uo.
 
Sorry for the late response. forgot to subscribe to this thread so didnt know there were any responses.

If it is not a typo then why the split?

I can undestand 230-400-1000v as that would be single phase, 3 phase and high voltage.

So why do they split it Uo for 230 400 and 1000?

Regs book is in the car so can't quote precise reg yet.

Just took my 17th 1st edition update today, there are quite a few changes!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Regs guide typo or not? - what is allowed disconection?!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
Inteificio,
Last reply from
MarkieSparkie,
Replies
11
Views
1,717

Advert

Back
Top