I was carrying out an EICR on a newly renovated property this week and discovered a few faults. However the guys that done the job are disputing the faults and saying that the work is ok. Basically need regs / reference numbers to support my claims.

First one was BS951 clamps being used as main earthing point which we know is not suitable but are there any regs specific to this?

And second one is a bit trickier, basically water pipe comes into the building, and is bonded, from here there is a short piece of plastic pipe (around 200mm) long and then joined onto copper pipe again where it disappears below floor. RCD CU is installed so I know no supplementary bonding is required but given that there is a break in the continuity so close to the source, then it becomes copper again, I thought there should be a bonding link installed between the two copper parts so as to continue the bonding as there is no guarantee that the copper pipe disappearing below the floor is not trailing the ground at points etc, which would then make the rest of the copper pipework in the house extraneous. Cannot get below floor to check. Would you guys agree with this and if so is there a reg to back this up?

Many Thanks
 
And if it tests out at below 1667?

Then supplementary bonding can be omitted as it would be classed as being 'effectively connected to the protective equipotential bonding'.

As long as it meets the other 2 points in reg 701.415.2 then it can be omitted.

But I know that you know this :smiley2:... so I feel like I've been led into the lions den and I await to be pounced on!!!!
 
We're not talking about SB though, relax mate I'm not that much of a barsteward really

Oh... I was quite looking forward to a discussion then Trev :sad3:! I'm still on a high from finding this fault (other thread) and feel that I could challenge D.Skelton or even Tony at the moment!!

..................10secs later


The moment has passed!
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Regs required for several faults
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19
Unsolved
--

Advert

Thread statistics

Created
brizospark,
Last reply from
dingledong,
Replies
19
Views
2,339

Advert

Back
Top