Hi guys and girls,

A client is moving their kitchen into another room that currently has a few sockets in it.

The sockets are currently on a ring final circuit that covers every socket in the house.

They've asked me to add sockets for the new kitchen so I am going to run a new kitchen circuit most of which can be done in trunking as it will be behind the units going in.

My question is am I able to replace the faceplates of the old sockets not being used/covered with a blanking plate and use maintenance free wago's inside so the ring for the rest of the house is not affected? (3 sockets I think that will end up behind units)

Thanks in advance
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members
Advertisement - Content continues below

richy3333

-
Mentor
Arms
Supporter
Esteemed
Yes if the wagos are rated appropriately. Your proposed solution would not be Maintainence Free so would need reasonable access for future I&T. Why not just remove the S/O’s and crimp and over-sleeve?
 

telectrix

-
Mentor
Arms
Esteemed
i would use the ideal in line splice connectors or push fit wagos. unless you are a builder, then choc block and ... plaster over.
 
  • Thread Starter Thread Starter
  • #6
I was looking at those inline splice, but wasn't sure which was better between them and the wago's, so would it be acceptable then to remove the S/O, use those inline splice, oversleeve and then patch up?
 

littlespark

-
Arms
Esteemed
Advent Win
Can the sockets not be utilised for under unit or kickboard lighting?
Marked accordingly so they know what isolates what
 

Baddegg

-
Arms
Supporter
Esteemed
Advent Win
If they not gonna be accessible I’d crimp and shrink em, trouble with wagos is they don’t class as MF if not in a wago box....not sure about the insure splice but won’t be to hard to check
 

Baddegg

-
Arms
Supporter
Esteemed
Advent Win
When they not in a wago box,always happy to be corrected but I’m sure that’s what I’ve read on wago website
 
  • Thread Starter Thread Starter
  • #11
When they not in a wago box,always happy to be corrected but I’m sure that’s what I’ve read on wago website
I never realised that, always thought the connectors were maintenance free regardless of what enclosure they were in, every days a school day as they say
 

richy3333

-
Mentor
Arms
Supporter
Esteemed
I was looking at those inline splice, but wasn't sure which was better between them and the wago's, so would it be acceptable then to remove the S/O, use those inline splice, oversleeve and then patch up?
No
 
Rather then the mf aspect, those cables will still be chased into the walls?

If so the connections will need to be accessible to create the zones
 

Baddegg

-
Arms
Supporter
Esteemed
Advent Win
I never realised that, always thought the connectors were maintenance free regardless of what enclosure they were in, every days a school day as they say
In the real world I doubt it makes much difference but then wago wouldn’t be able to sell they boxes......their ball their rules I spose :)
 