It's sort of obvious isn't it that you can't fit brass links ?

Even at 13amp it was never a great system in terms of overload
The solid links were available. I came to see if anyone had still come across them. I know there is no need for them as 15A fuseless round pin plugs are available. But those manufacturers (mainly from China) again...
 
You can also get fused 15A plugs but the British Standard only permits a maximum 5A fuse, solid link time?
 
You can also get fused 15A plugs but the British Standard only permits a maximum 5A fuse, solid link time?
You can still use BS 546 style round pin fuseless plugs and sockets according to BS7671. These are 2A, 5A and 15A, as long as the socket is shuttered.

15A round pin fuseless plugs are not allowed directly on final ring circuits only square pin 13A fused. See: BS7671. section: 433.1.204.

BS 546, 2A, 5A and 15A are permitted on radials, and that is also a radial spur off a final ring. See: BS7671. section: 553.1.3 Table 55.1.

So you can have a 13A FCU off a Final Ring Circuit, with a 15A fuseless round pin BS 546 say behind a washing machine. Which is the best way to go in such a situation, so the fuse is not inaccessible. And to keep a 13A plug from overheating around the fuse in a continuous 13A current draw.

You can have a 15A mcb with a number of BS 546 15A fuseless plugs on a radial in your home. All legal and above board.
 
Last edited by a moderator:
Perhaps you might explain the reasoning behind wanting to explore this particular line of thinking, given the infrequent occurrence of blown appliance fuses? It seems as though many respondents, myself included, struggle to comprehend the problem you're seeking to overcome.
 
Perhaps you might explain the reasoning behind wanting to explore this particular line of thinking, given the infrequent occurrence of blown appliance fuses? It seems as though many respondents, myself included, struggle to comprehend the problem you're seeking to overcome.
I recapped that a few times in the thread. People do not read the whole thread just the last couple of posts.
But you might have noticed this in my last post:

"And to keep a 13A plug from overheating around the fuse in a continuous 13A current draw."

This was used on a tumble dryer. Moulded a well. This rarely happens using 15A round pin.

1635000904677.jpeg
 
Last edited by a moderator:
I recapped that a few times in the thread. People do not read the whole thread just the last couple of posts.
But you might have noticed this in my last post:

"And to keep a 13A plug from overheating around the fuse in a continuous 13A current draw."

This was used on a tumble dryer. Moulded a well. This rarely happens using 15A round pin.

View attachment 91298
That doesn't look like a fuse issue as both pins have suffered thermal damage.
 
All appliances cheap and expensive should be safe. Fixing a superior plug minimises fire risk, if faulty manufacture.
 