First visit here so hi everyone.

My problem is I have just gone to do add a few sockets for someone and upgrade the fuse board. Done some basic checks first and discovered an existing ring main had a very high zs (3.4). Checked the Ze and was fine (.2 for tns). Assumed there would be a dodgy earth at one of the sockets but all earths seemed fine. Decided to check the R1R2 and there is only one earth cable at the board.

This is an old bungalow and the ring circuit consists of stranded live and neutral but the earth is run as a radial circuit from the board. I can't connect the outgoing live to incoming earth and vice versa so what do you do in this case? Am i getting odd readings because the earth isn't a ring? I just thought i'd see if there was an obvious explanation before i crawled in the loft to follow the earth.

Thanks
 

Reply to ri/r2 weird in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
961
Carrying out an EICR and came across a ring final circuit wired to the first of six metal clad sockets in 2.5mm 5 core SWA. Obviously 2 cores for...
Replies
5
Views
992
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
886

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top