I’ve done some labouring support work for sparks in the past (joiner by trade) and have a qualified spark installing an electric shower for me. To save him time I’m going to run the cable. Using 10mm. Walls and floors not easily accessible and shower is about 25m of wire from consumer unit. Easiest way is to go outside, up about 10 foot of wall then back in through the roof. If in galvanised trunking is this acceptable?
 
What size is the load? What's the environment like? (Ambient temperatures, insulation along run etc).

(also begs the question, if you have a spark on the job for you, why wasn't he your first goto for posing the question)
 
So did I! Exactly the same!
to be fair, it was her doll's house, and I scaled the 10mm down to bell wire...
Only so much you can run off 3 AA batteries!
Could have used one of those bicycle lamp batteries.
 
What size is the load? What's the environment like? (Ambient temperatures, insulation along run etc).

(also begs the question, if you have a spark on the job for you, why wasn't he your first goto for posing the question)

The load? Can’t think of a shower which will need more than a 10mm cable bud regardless of environment in the average house, your second question can be answered easily, there is no spark lol
 
10mm T&E standard has low UV tolerance and shouldn't be the cable of choice for external work especially if in direct sunlight.

I would consider an armoured which can be converted back at the load end if required to a more suitable cable for terminating into the shower isolation switch.

I have yet to come across a house where I couldn't route a cable internally, if floors need to come up and walls need to be drilled or chased then that is the case, if chasing walls though ensure of routing within prescribed zones permitted.
 
Or at least put it in some black plastic conduit.
 
PVC T&E is not suitable for installation outside because
a) it is not UV stabilisised and may break down after a while
b) constant frost/heat/frost/heat cycles will kernacker it

Run in conduit it is fine. For 10mm you'll probably need 25mm though....
Better to run 10mm SWA for that sort of job.
 