Discuss Running 10mm T&E externally? in the UK Electrical Forum area at ElectriciansForums.net
I’ve done some labouring support work for sparks in the past (joiner by trade) and have a qualified spark installing an electric shower for me. To save him time I’m going to run the cable. Using 10mm. Walls and floors not easily accessible and shower is about 25m of wire from consumer unit. Easiest way is to go outside, up about 10 foot of wall then back in through the roof. If in galvanised trunking is this acceptable?
What size is the load? What's the environment like? (Ambient temperatures, insulation along run etc).
(also begs the question, if you have a spark on the job for you, why wasn't he your first goto for posing the question)
The load? Can’t think of a shower which will need more than a 10mm cable bud regardless of environment in the average house, your second question can be answered easily, there is no spark lol
10mm T&E standard has low UV tolerance and shouldn't be the cable of choice for external work especially if in direct sunlight.
I would consider an armoured which can be converted back at the load end if required to a more suitable cable for terminating into the shower isolation switch.
I have yet to come across a house where I couldn't route a cable internally, if floors need to come up and walls need to be drilled or chased then that is the case, if chasing walls though ensure of routing within prescribed zones permitted.
PVC T&E is not suitable for installation outside because
a) it is not UV stabilisised and may break down after a while
b) constant frost/heat/frost/heat cycles will kernacker it
Run in conduit it is fine. For 10mm you'll probably need 25mm though....
Better to run 10mm SWA for that sort of job.
Is there any particular problem with using ho7 flex for the whole run from CU to isolator? It's got superior properties to T and E. I know people get wound up about using 'flex' for fixed wiring, but not sure why. Seems to be the norm on the continent, and none of this reduced cpc nonsense we have!
If I were to do the job, I'd use SWA, if only to avoid critisism from any following sparks about inappropriate use of flex...but is that actually the best solution?
Sparks walking the inca trail for the next 2.5 weeks and pretty uncontactable. Thanks. It’s a 7.0Kw shower unit. Was planning on putting the bit that sits outside in galvanised trunking.
Hey, it's only got to be able to carry fault current for less than 0.1s in most cases. Most of the time they are actually well oversized!! :)
thanks for the reply. Is it ok to run it externally in some form of trunking for about 10ft? The house has 80cm thick stone walls so pretty tricky to channel/go under floors etc.
Reply to Running 10mm T&E externally? in the UK Electrical Forum area at ElectriciansForums.net
I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known...
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Hello ladies and gents , Simple question , where in the regs book would It discuss or what does it say about clipping direct 1.5mm t&e in the...
I have a TPN board that will feed 8-10 sub boards. The loads on each board are negligible 5-10 amps peak but mostly 1-2 amps. The distribution...