I have had my kitchen rewired and plastered. I have had a 6mm t+e on a dedicated 32a circuit for a 60cm electric cooker. In hindsight, had i known at the time, i would have asked for a10mm cable to future proof the installation. The cables run from the consumer unit in the attached garage, into the single storey flat roof joists, to the wall of the kitchen. The cables in the garage are in trunking (to keep them tidy). I have been told that if 6mm t+e is installed using method C it is good for a 40a fuse. As things stand, because of the trunking, the installation method is method B. My question is, if just the cooker cable was taken out of the trunking, then clipped to the brickwork, and carries on into the kichen roof, would this then constitute method C. A larger 90cm cooker could then be installed if so desired in the future.
 
How long is the trunking and how many other cables are in it?
 
3.4m of trunking with15 other cables in it.
OK. There are some will argue that's not brilliant, and there are some (like me) who will argue that in practice that's fine. So if there's an easy way to do as you say and clip it directly to the block instead then that would be better.
 
i don't understand what you are saying.
I'm saying that the easiest way to solve your conundrum without having to go into a whole heap of intracacies and maths is to do as you suggested and take it out of the trunking and clip direct (method C).
 

Reply to 40a circuit breaker6mm t+e in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have had my kitchen rewired ready for a new kitchen. I was originally going to have a gas cooker so a 3 pin 13a socket was left on the end of...
Replies
2
Views
369
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
547
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
785

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock