cliffed

~
Arms
having probs with Fire alarm.Its a sense alarm 2 wire,mcp's,detectors & sounders.
Goes into Fire mode,even when only 3 points are on circuit.
Are all their sounders compatible with the system,it's difficult to understand properly ,we have sounders,which are alarm sense,not the sounder & base ones,on their diagram.
Commissioning guy,going round in circles.
 
What happens with nothing other than the end of line device connected across the panel terminals ?
 
having probs with Fire alarm.Its a sense alarm 2 wire,mcp's,detectors & sounders.
Goes into Fire mode,even when only 3 points are on circuit.
Are all their sounders compatible with the system,it's difficult to understand properly ,we have sounders,which are alarm sense,not the sounder & base ones,on their diagram.
Commissioning guy,going round in circles.
Have you connected the bases in parallel (if using standard bases)? Both in and out should be connected to L1 in +ve and L2-ve. Not how you would connect a coventional base using in and out.
 
Split the circuit down by moving the EOL resistor, once you've narrowed it down to a section wago a detector at a time.
 
As Lee said, break the circuit down & bridge each head or call point one at a time.
I normally keep a set of short jump leads in my kit to quickly bridge things out.
 
Are you using sounder bases or have a sounder circuit? All the gear is alarmsense? EOL capacitor for detector circuits and EOL resistor for sounder circuits? If using separate sounders are they polarised?
 
Are you using sounder bases or have a sounder circuit? All the gear is alarmsense? EOL capacitor for detector circuits and EOL resistor for sounder circuits? If using separate sounders are they polarised?
No sounder circuit,all on same circuit,sounders are not base sounders,all alarm sense equipment.They are not polarity sensitive
 