Discuss Sequence of tests in guidance note 3 (initial verification) in the UK Electrical Forum area at ElectriciansForums.net

mak

-
Reaction score
10
How come the sequence of tests in guidance note 3 is that the Zs test comes before the PFC test?

Isn't it normal to do PFC test before the Zs test? Because then you can do your PFC test, put the board cover on and energize the board without coming back to do the PFC test.
 
So how would you do your ZS test at board...Think about it...Disconnect Main Earth do ZE test Reconnect Main Earth Do ZS.....How can you do a ZS at DB if cover is on
 
So how would you do your ZS test at board...Think about it...Disconnect Main Earth do ZE test Reconnect Main Earth Do ZS.....How can you do a ZS at DB if cover is on
I would measure Zs on sockets using a plug adaptor and calculate the rest?
 
Do you mean Ze, the impedance at the board, before you do the Zs, impedance at end of circuit?

In practically all cases you measure Zs/Ze along with the related PFC using your MFT.
 
How come the sequence of tests in guidance note 3 is that the Zs test comes before the PFC test?

Isn't it normal to do PFC test before the Zs test? Because then you can do your PFC test, put the board cover on and energize the board without coming back to do the PFC test.

Can you post a picture of the list of tests you are referring to, there may be a detail you have missed.

Which Zs test is it referring to? The Zs at the DB or the Zs of final circuits?

PFC is calculated and displayed by the test meter for every loop impedance test, it's not possible to carry them out as seperate tests.
 
PFC is calculated and displayed by the test meter for every loop impedance test, it's not possible to carry them out as seperate tests.

not on all meters. on the megger 1552/3 they are separate tests. don't know about the 1700 series.I can't afford anything that fancy.
 
not on all meters. on the megger 1552/3 they are separate tests. don't know about the 1700 series.I can't afford anything that fancy.

Really? That seems a bit backwards considering that the meter doesn't measure the PFC, it measures the loop impedance and voltage and calculates PFC from that.

I've got a 1700 series and that displays PFC on the same screen, on my seperate high resoloution loop tester you press a button to cycle the display to show PFC.
I think the fluke and Kewtech I used in years gone by were the same, press a button to cycle the display and show PFC.

I just assumed they were all the same.
 

if you zoom the pic, it shows separate tests for pfc. both on hi current and no-trip.

also posted link as this looks matbe a good buy for any trainee on a limited budget.
 
if you zoom the pic, it shows separate tests for pfc. both on hi current and no-trip.
A bit odd as the measurement (as already pointed out) basically reveals Zs from observing delta-V while switching a known delta-I, and then from the voltage, computes PFC = V / Zs

Maybe to have an extra "feature" to sell?

Maybe the display lacked the space to show both simultaneously?
 
Can you post a picture of the list of tests you are referring to, there may be a detail you have missed.

Which Zs test is it referring to? The Zs at the DB or the Zs of final circuits?

PFC is calculated and displayed by the test meter for every loop impedance test, it's not possible to carry them out as seperate tests.
I meant Zs of final circuits. Not the Zs at DB for which you need the board to be open.
After insulation resistance I'd do supply polarity, Zs at DB, then PFC, then put the lid back on, energise the board, then do the Zs of final circuits.
[automerge]1596713360[/automerge]
if you followed the correct Sequence of tests you just do You Earth Fault Loop Impedance Ze at the board and add your result to your R1+R2 then do your PFC tests.
One person says Ze another Zs at DB can we please come to a common denominator? If it's a DB test, then it's a Zs at DB. And that's not even my question.
[automerge]1596714800[/automerge]
Do you mean Ze, the impedance at the board, before you do the Zs, impedance at end of circuit?

In practically all cases you measure Zs/Ze along with the related PFC using your MFT.
I'm not talking about Ze/Zs at DB at all. It's a test done on a dead board right? So is PFC test i.e. I don't need to energize the board. Only for the Zs of final circuits I need to energize the board. So I thought would it make sense to change the sequence, do the PFC at DB then the Zs of final circuits.
 
Last edited:
For what it’s worth once I measure Ze , I reconnect the earthing conductor and immediately perform a pefc With all parallel paths in place and then a pscc test and record the higher value as the PFC at the origin of the installation.
To me it’s an obvious thing to do while you are physically already at the CU position.
The sequence of tests in gn3 has protection by automatic disconnection of supply to be verified before earth fault loop impedance of the external earth supply and pfc testing anyway.
 
Last edited:
I'm not talking about Ze/Zs at DB at all. It's a test done on a dead board right? So is PFC test i.e. I don't need to energize the board. Only for the Zs of final circuits I need to energize the board. So I thought would it make sense to change the sequence, do the PFC at DB then the Zs of final circuits.
If it is a dead board then you can't measure the supply PFC - that (i.e. Ze) is a property of the supply itself.

You might chose to assume values such as 0.35 / 0.8 ohm for TN-C-S / TN-S and then estimate you Zs by adding R1+R2, but usually the whole point of determining the supply PFC is to verify that the switchgear/MCBs/etc are able to safely interrupt a fault.

The Zs / end of circuit PFC is important as well, it will almost certainly be lower than the DB PFC, but it will allow you to verify that your circuit's OCPD can disconnect fast enough.

To be fair. in most domestic cases you will never see a scary PFC that presents problems, but if you are inspecting and find a board with rewirable fuses you really ought to verify they can break the supply that is actually present. They might not!
 
I meant Zs of final circuits. Not the Zs at DB for which you need the board to be open.
After insulation resistance I'd do supply polarity, Zs at DB, then PFC, then put the lid back on, energise the board, then do the Zs of final circuits.
[automerge]1596713360[/automerge]

One person says Ze another Zs at DB can we please come to a common denominator? If it's a DB test, then it's a Zs at DB. And that's not even my question.
[automerge]1596714800[/automerge]

I'm not talking about Ze/Zs at DB at all. It's a test done on a dead board right? So is PFC test i.e. I don't need to energize the board. Only for the Zs of final circuits I need to energize the board. So I thought would it make sense to change the sequence, do the PFC at DB then the Zs of final circuits.

In which case yes you would normally carry out the Zs at the DB, PEFC and PSCC tests before closing the main switch of that DB on initial verification.

You are correct that Ze and Zs are different things, sadly on the forum you will often see them used interchangeably.

Zs and PFC are live tests carried out on a live supply, they are not dead tests.
The main switch of the DB does not need to be closed, but the supply up to the main switch does need to be energised.
 
I don't think theres any requirement for PFC at the end of the circuit the current will decrease you want the Maximum PFC to make sure your protective devices could handle it.

then Ze at board and add to your R1+R2 at furthest point or highest reading etc to get you Zs to make sure ADS can be archived.

of-course you can do direct direct Zs measures at the end of the circuit.

and as was pointed out to me on here Zs at DB is only really useful for a Sub-consumer unit.
 
and as was pointed out to me on here Zs at DB is only really useful for a Sub-consumer unit.
I guess I'm thinking commercial sites, where you get Ze of Ze of Ze so only the main is true Ze, the rest are Zs at Db is it not? If you were given Ze by the DNO and measured Ze at DB, and they would differ, would that mean the board is sub main? But in any case which of the two "Ze" would you choose to calculate the Zs of final circuits?
 
I guess I'm thinking commercial sites, where you get Ze of Ze of Ze so only the main is true Ze, the rest are Zs at Db is it not? If you were given Ze by the DNO and measured Ze at DB, and they would differ, would that mean the board is sub main? But in any case which of the two "Ze" would you choose to calculate the Zs of final circuits?
Do you do tutorials? :cool:
 

Reply to Sequence of tests in guidance note 3 (initial verification) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
818
Because none of us are beyond schoolboy errors.......... Doing some events kit testing over the weekend, some larger metal stand distro panels...
Replies
7
Views
1K
Hi this is my first post, I’m looking for some advice I’m doing my Inital verification course as part of my NVQ. I’ve passed the practical part...
Replies
2
Views
1K
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
619
Hello, I’ve got my AM2S coming up and I’ve been revising like mad but I’m stuck on something. I’ve read that it’s a 3 phase board with just...
Replies
11
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock