Hello all,
I've spent the last 24 hours or so reading a few quite fascinating threads on fault finding some of which sounded incredibly similar to my scenario, and I was hoping to get some advice. To be clear, I am the customer, not an electrician, and I am absolutely not expecting any advice on DIY or how to fix. I've already had one person out, and I'm left a bit stumped, and would love to get some advice from the clearly incredibly knowledgeable folks on these forums.
Story is, I have a problem with my shower. Have had the electrician out today who did a number of tests and was unable to pinpoint the root cause.
First noticed something was wrong when touching the shower tap handle the other night and felt a sharp electric sting, it must be a very low current as it is a bit of an accident that I felt it at all, I could only feel it on a broken part of skin that was also wet on my thumb. Even with a wet hand standing in the water my unbroken skin cannot detect it. Still, it has obviously made me extremely uneasy.
First thing I did immediately as I do have a digital multimeter (for electronics and guitar wiring hobby work), was to measure the voltage across the path that I was able to feel it on, that is from the shower tap metalwork directly into the water in the shower waste, I got a reading of 20v. So confirmation I wasn’t imagining it.
Today RCDs were tested, bonding continuity tested within the property and some insulation resistance tests carried out. RCDs were apparently fine both tripping at between 24 and 26 mA, many circuits insulation resistance was excellent (reading 999Mohm +) but with some cable runs reading as low as 60Mohm which I was advised is poor in comparison but acceptable. Continuity between my shower taps and earth point in the CU was measured as good, and bonding is in place on the pipework in the flat as expected.
In terms of identifying the source of the voltage, electrician flipped the breakers for various circuits to see if they had an influence on the voltage reading at the shower:
Lighting circuit only: 12v
Sockets circuit only: 10v
Smoke detector circuit only 9v
With all circuits on the highest reading he got with his MFT vs my cheap little multimeter was 24v at the shower.
The conclusion we came to today, is that where the plastic soil pipe meets metal which it eventually does somewhere in the building as I can see all the soil pipes in the underground car park, there is a difference in potential between my earth and that pipework’s earth (if that makes sense?) I think one of the tests that was done was checking for that 24v to appear between the shower taps and the supply earth with the bonding disconnected (which it did not).
From my (limited) understanding there are two separate issues here:
1. Potentially a bonding issue between my flat (And presumably all flats) and the communal metal soil pipework
2. Buildup of earth leakage current that is then being transferred to the soil pipe earth (via me!)
The electrician was incredibly kind and persistent and seemed genuinely curious and determined to find the issue, he also called NICEIC helpline with me to ask them for some testing advice, but, without a definitive resolution I still feel incredibly uneasy about the electrical condition of the flat.
I would really appreciate any and all advice, but I also have some specific questions for my understanding.
1. The leakage current so far doesn't seem to come from any one source based on the isolated breaker tests he did so what could be some potential explanations of this?
2. Could purely capacitive coupling from multiple circuits even cause enough of a current that it could be felt (albeit with a wet, cut finger, the most conductive skin scenario) I ask because I know my digital multimeter (fluke 101) does not have a low impedance mode so does pick up so called "phantom" voltage, but as soon as there is a load across this measurement the voltage goes away, and I thought that was the only type of voltage one might see from capacitive coupling, certainly not something I could actually feel.
3. Is testing the resistance between the metal soil stack and my earth a sensible thing to ask the next electrician to do?
4. Just incase the next electrician also doesn't find a definitive answer, does anybody have any recommendations for some true fault finding geniuses in the East London area? I'm already one callout down cash wise and whilst I'm glad it appears there are no glaring faults nor 240v flowing anywhere so I'm probably not going to die anytime soon, I would like absolute certainty that everything is safe.
Thanks all
I've spent the last 24 hours or so reading a few quite fascinating threads on fault finding some of which sounded incredibly similar to my scenario, and I was hoping to get some advice. To be clear, I am the customer, not an electrician, and I am absolutely not expecting any advice on DIY or how to fix. I've already had one person out, and I'm left a bit stumped, and would love to get some advice from the clearly incredibly knowledgeable folks on these forums.
Story is, I have a problem with my shower. Have had the electrician out today who did a number of tests and was unable to pinpoint the root cause.
First noticed something was wrong when touching the shower tap handle the other night and felt a sharp electric sting, it must be a very low current as it is a bit of an accident that I felt it at all, I could only feel it on a broken part of skin that was also wet on my thumb. Even with a wet hand standing in the water my unbroken skin cannot detect it. Still, it has obviously made me extremely uneasy.
First thing I did immediately as I do have a digital multimeter (for electronics and guitar wiring hobby work), was to measure the voltage across the path that I was able to feel it on, that is from the shower tap metalwork directly into the water in the shower waste, I got a reading of 20v. So confirmation I wasn’t imagining it.
Today RCDs were tested, bonding continuity tested within the property and some insulation resistance tests carried out. RCDs were apparently fine both tripping at between 24 and 26 mA, many circuits insulation resistance was excellent (reading 999Mohm +) but with some cable runs reading as low as 60Mohm which I was advised is poor in comparison but acceptable. Continuity between my shower taps and earth point in the CU was measured as good, and bonding is in place on the pipework in the flat as expected.
In terms of identifying the source of the voltage, electrician flipped the breakers for various circuits to see if they had an influence on the voltage reading at the shower:
Lighting circuit only: 12v
Sockets circuit only: 10v
Smoke detector circuit only 9v
With all circuits on the highest reading he got with his MFT vs my cheap little multimeter was 24v at the shower.
The conclusion we came to today, is that where the plastic soil pipe meets metal which it eventually does somewhere in the building as I can see all the soil pipes in the underground car park, there is a difference in potential between my earth and that pipework’s earth (if that makes sense?) I think one of the tests that was done was checking for that 24v to appear between the shower taps and the supply earth with the bonding disconnected (which it did not).
From my (limited) understanding there are two separate issues here:
1. Potentially a bonding issue between my flat (And presumably all flats) and the communal metal soil pipework
2. Buildup of earth leakage current that is then being transferred to the soil pipe earth (via me!)
The electrician was incredibly kind and persistent and seemed genuinely curious and determined to find the issue, he also called NICEIC helpline with me to ask them for some testing advice, but, without a definitive resolution I still feel incredibly uneasy about the electrical condition of the flat.
I would really appreciate any and all advice, but I also have some specific questions for my understanding.
1. The leakage current so far doesn't seem to come from any one source based on the isolated breaker tests he did so what could be some potential explanations of this?
2. Could purely capacitive coupling from multiple circuits even cause enough of a current that it could be felt (albeit with a wet, cut finger, the most conductive skin scenario) I ask because I know my digital multimeter (fluke 101) does not have a low impedance mode so does pick up so called "phantom" voltage, but as soon as there is a load across this measurement the voltage goes away, and I thought that was the only type of voltage one might see from capacitive coupling, certainly not something I could actually feel.
3. Is testing the resistance between the metal soil stack and my earth a sensible thing to ask the next electrician to do?
4. Just incase the next electrician also doesn't find a definitive answer, does anybody have any recommendations for some true fault finding geniuses in the East London area? I'm already one callout down cash wise and whilst I'm glad it appears there are no glaring faults nor 240v flowing anywhere so I'm probably not going to die anytime soon, I would like absolute certainty that everything is safe.
Thanks all