Hello all,
I've spent the last 24 hours or so reading a few quite fascinating threads on fault finding some of which sounded incredibly similar to my scenario, and I was hoping to get some advice. To be clear, I am the customer, not an electrician, and I am absolutely not expecting any advice on DIY or how to fix. I've already had one person out, and I'm left a bit stumped, and would love to get some advice from the clearly incredibly knowledgeable folks on these forums.
Story is, I have a problem with my shower. Have had the electrician out today who did a number of tests and was unable to pinpoint the root cause.
First noticed something was wrong when touching the shower tap handle the other night and felt a sharp electric sting, it must be a very low current as it is a bit of an accident that I felt it at all, I could only feel it on a broken part of skin that was also wet on my thumb. Even with a wet hand standing in the water my unbroken skin cannot detect it. Still, it has obviously made me extremely uneasy.
First thing I did immediately as I do have a digital multimeter (for electronics and guitar wiring hobby work), was to measure the voltage across the path that I was able to feel it on, that is from the shower tap metalwork directly into the water in the shower waste, I got a reading of 20v. So confirmation I wasn’t imagining it.
Today RCDs were tested, bonding continuity tested within the property and some insulation resistance tests carried out. RCDs were apparently fine both tripping at between 24 and 26 mA, many circuits insulation resistance was excellent (reading 999Mohm +) but with some cable runs reading as low as 60Mohm which I was advised is poor in comparison but acceptable. Continuity between my shower taps and earth point in the CU was measured as good, and bonding is in place on the pipework in the flat as expected.
In terms of identifying the source of the voltage, electrician flipped the breakers for various circuits to see if they had an influence on the voltage reading at the shower:
Lighting circuit only: 12v
Sockets circuit only: 10v
Smoke detector circuit only 9v
With all circuits on the highest reading he got with his MFT vs my cheap little multimeter was 24v at the shower.
The conclusion we came to today, is that where the plastic soil pipe meets metal which it eventually does somewhere in the building as I can see all the soil pipes in the underground car park, there is a difference in potential between my earth and that pipework’s earth (if that makes sense?) I think one of the tests that was done was checking for that 24v to appear between the shower taps and the supply earth with the bonding disconnected (which it did not).
From my (limited) understanding there are two separate issues here:
1. Potentially a bonding issue between my flat (And presumably all flats) and the communal metal soil pipework
2. Buildup of earth leakage current that is then being transferred to the soil pipe earth (via me!)
The electrician was incredibly kind and persistent and seemed genuinely curious and determined to find the issue, he also called NICEIC helpline with me to ask them for some testing advice, but, without a definitive resolution I still feel incredibly uneasy about the electrical condition of the flat.
I would really appreciate any and all advice, but I also have some specific questions for my understanding.
1. The leakage current so far doesn't seem to come from any one source based on the isolated breaker tests he did so what could be some potential explanations of this?
2. Could purely capacitive coupling from multiple circuits even cause enough of a current that it could be felt (albeit with a wet, cut finger, the most conductive skin scenario) I ask because I know my digital multimeter (fluke 101) does not have a low impedance mode so does pick up so called "phantom" voltage, but as soon as there is a load across this measurement the voltage goes away, and I thought that was the only type of voltage one might see from capacitive coupling, certainly not something I could actually feel.
3. Is testing the resistance between the metal soil stack and my earth a sensible thing to ask the next electrician to do?
4. Just incase the next electrician also doesn't find a definitive answer, does anybody have any recommendations for some true fault finding geniuses in the East London area? I'm already one callout down cash wise and whilst I'm glad it appears there are no glaring faults nor 240v flowing anywhere so I'm probably not going to die anytime soon, I would like absolute certainty that everything is safe.
Thanks all
Hello all,
Thanks all
If the shower waste is metal then this might be an Extraneous Conductive Part.
The soil waste should also be checked most likely shower waste is connected to the soil stack.
I am surprised the Electrician didn't do the test since this was postulated as a possibility?
It would be difficult in your scenario to visually check this most likely it is picking up Earth Potential in some part of the building.
Did the electrician isolate the supply to your flat, not just individual circuits and take any measurements?
Don't get distracted or let anyone else get distracted on the exact location of the issue.
You have an electrical fault in your flat, it may be as a result of a fault on your electrical installation or may be an issue caused by another flat.
Until the fault is located and fixed you should avoid using the shower.
Don't try and repeat the fault by touch, the 20v might might be 240v next time.
The current up to the point an Rcd / Rcbo trips can be very painful, been there done that, as have many others on here.
Is the shower electric and or does it it have boost pump of any sort connected to the water supply to it or to the flat?
It's not uncommon for flats to have a direct mains water supply to the kitchen tap and tank stored boost pumped supply to all other taps / outlets to avoid high demand on the incoming water supply.
Thanks both,
The shower waste is plastic, to clarify, the main soil stack inside my flat is also plastic, I just know that at some point it transitions to metal as in the basement the large metal pipework running from all the flats is visible. Quite where this transition is I don't know yet but will need to find this out.
The water appears to be the only conductor creating a path from my shower to the mystery point currently presumed to be that pipework. The voltage reading peaks with the water running, then as the shower is stopped and the water running down the waste dissipates the voltage gradually backs off eventually completely.
I'm on the 3rd floor so I'm not sure how possible/useful it is to test against the point where I know the waste ends up being metal, even with a 50m wander lead like he had yesterday? And he didn't have any ideas for where to look closer to me, apart from we did stick an inspection camera down the shower waste just to verify that it was plastic at least for the immediate run (and no stray screws/ nails poking in from somewhere etc.) but that was only about a metre or so checked.
I don't want to say I'm 100% sure that he didn't isolate, but if I had to guess I would say no, as he didn't go into the service head/ meter cupboard which is in a communal hallway behind a fire brigade lock. Inside my property he only had access to the CU.
Right, thank you, I will make sure to push this until I get a definitive answer. I forgot to clarify that in the voltage readings he took (and that I also did myself first thing) with everything switched off on the CU the voltage measured drops to nearly 0. So he said it must be coming from inside my flat.
Good to know that whilst the RCD should protect me, its still not going to be nice if there's a fault.
All the hot water including the shower is fed from an electric PulsaCoil thermal storage type thing (not sure if one would call it a boiler).
Thanks both,
Thanks for clearing that up.
I would get the PulsaCoil checked out to eliminate it as the source.
Waiting to hear back from another firm who advertise themselves for testing and fault finding specifically.
In the meantime, I did some more thinking, reading and inspected the shower and it just didn't make sense to me that a bit of metal pipework some many metres away could be closing a circuit so quickly as soon as I run some water in my shower (there would be no column of water , other flats not backed up, drains very quickly.
Did another quick check with the meter, and for the first time, had the meter on the shower before turning the tap on, and noticed that the split second the water reached the waste where the other probe was sitting, it jumped up to 20v. Way before any meaningful amount of water had time to flow down the waste and meet this mysterious other side of this potential.
Then, I had an odd thought, (as I said before, not an electrician, but work with guitars, amplifiers and small electronics projects so have some understanding of electrical concepts) could the plastic shower tray be acting as a dielectric and could the pool of water be capacitively coupled to something underneath?
So I dried the trap, covered the waste hole with a wide rubber plug to completely block it, and filled up the shower tray. Hey presto, 28v on the meter. I assume the slightly higher voltage was because I had filled up the entire shower tray so there was better coverage over the entire plate in this capacitor analogy. Measured a resistance of 290kilohm which if you round up a tad is 0.1mA, which I think is small enough to explain why I could only feel it on a tiny bit of broken skin, and not soaking wet skin.
This would also explain why the electrician couldn't find anything seriously wrong anywhere. If the source is just a few mA of leakage current from various appliances (I think he measured 4-5mA of leakage), and nothing is 'broken' but the water in my shower tray is mysteriously capacitively coupled to something else with a path back to earth (which is not bonded anywhere to my earth) then there would be nothing really to find.
The only question to ask, is, is this possible or is it completely mental? I don't know how else to explain the readings I'm getting into an isolated pool of water in a plastic shower tray.
Got access to underneath the shower.
Metal stud work in the flat all around, shower tray is surrounded on 3 sides by the metal bottom plate of this studwork. Reading from one stud to earth was 33v, and the other stud on the opposite wall was 28v, no continuity between them.
I understand from some reading that regs do not normally recommend bonding stud work as it is isolated by the plasterboard, but out of curiosity I clipped a temporary run of cable between the two studs, and an existing bonding point on pipework, did the same water test and the voltage completely disappeared, my meter read 0.24v!
So I think the best theory is:
  • Metal stud work picks up an induced voltage from live cables running along them
  • Metal stud work is capacitively coupled to pooled water in shower tray
  • Current flowed to the earthed shower via me, and I only felt it because of the dramatically reduced resistance of my body at that point (stood in water, wet very small point of broken skin on my thumb)
But I have to admit, this is totally bizarre, and never heard of anything like it in anything that I read.
Will ask the electrician to verify that the stud work is not live, but from my measurements it certainly doesn't seem to be.
This reminds me of a fatality some years ago.
Just found a link to the discussion
Some of it is not very helpful but the point is that a fault can lead to death if not found and fixed correctly.
Thread 'Emma Shaw Electrocution.'
https://www.electriciansforums.net/threads/emma-shaw-electrocution.71400/
Here is an article about it
Thanks for flagging the potential severity of it James, that’s exactly why I want to get to bottom of it properly, hence this thread and contacting another electrician (hopefully they get back to me on Monday). Thanks for everyone’s input so far it is much appreciated.
It seems the most important things to ask my electrician to answer definitively are:
1. Is the voltage I’m reading on the studwork an induced voltage from the cable running along it or an actual fault.
2. If it is just induced voltage, whether it makes sense to bond the studs around the shower, because it was unpleasant to touch even though minor.