In my current smart home project I have a total load in the panel of around 30A. Should I just use one big PSU rated at 30A or split the load across say three 10A PSU's?
 
30A? that's about 7kWH, that's about £1/hour, or £168/week. i would not call that a smart home, i'd call it a money spinner for supplier. :(
 
So if the PSU fails, it all fails?
Yeah, that was my big concern too, hence I thought splitting it across a number of PSU's might be more sensible.
30A? that's about 7kWH, that's about £1/hour, or £168/week. i would not call that a smart home, i'd call it a money spinner for supplier. :(
Sorry, didn't give you enough info - loads are all 24v and 30A (less than 800w) is the maximum assuming I switch every single light and LED strip on at the same time at maximum brightness.
 
Also remember to include fuses or other protection for the wiring and strip. Splitting into 10a PSUs would also mean the overload protection on the PSUs would protect each circuit at 10a. I watched an interesting video recently about short circuit current and overload protection for LED strip. It's sonething people often forget.
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Sussex

Thread Information

Title
Should I split PSU load?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
Rob99,
Last reply from
shaun1,
Replies
7
Views
1,262

Advert

Back
Top