Doing some calculations, I don’t agree with your tenants electrician. A 6mm cable, clipped direct will be absolutely fine on a 40amp mcb. The only issue is if the shower circuit is not on an RCD. Providing the run isn't miles and miles.
Putting a 32amp mcb in the circuit will just cause annoying tripping as the 8.5 kw shower will draw around 36amps.
Sounds like the electrician needs to look at the books a bit
Agree it does not need changing, and probably better not to. Not so sure 36 amps would cause the overload part of the breaker to nuisance trip though, looking at the curve for it.
That would be one seriously long shower!
apart from all the good advice given so far, as long as the 6.0mm is installed as ref. method C, i.e. it can safely carry 47A, ( Ib<Iz ) then aas the shower is a fixed load, overcurrent protection is not required so a 50A MCB could be installed. 433.3.1 (ii). (BYB 17th).
I mean, going off this even if its in trunking on its own, then it will be alright on a 40A.
Ask her to get her electrician to put it in writing also quoting BS as well as his or her part P approval body.
Then armed with the said information ring the help desk of the said body (they all have a help desk), quote their number etc and speak to them they will give you 100% the answer. Ensure your tennant tells sparky what you are doing. If he is fully approved and he’s correct he will not hesitate in supplying the information.
Thank you Tom for the advice seems like plan.
Regards Chris
One things for sure they should be greatful they have got a landlord that cares, the fact you are investigating there concerns rather than just saying hey it works what u complaining about shows you care not to mention new cooker
Thank you for your comments, I just want my tenant to have a safe home they can enjoy after all the do pay the rent.
Regards Chris
I have since found out from the tenant that he did not even go upstairs to look at the shower so has no idea about it's power rating.
What is even more worrying he said that instead of connecting the cooker with 6mm cable he should really be using flexible multi strand cable like on her kettle or halogen cooker.
I have never heard of this can anyone please enlighten me.
Regards Chris
What is even more worrying he said that instead of connecting the cooker with 6mm cable he should really using flexible multi strand cable like on her kettle or halogen cooker.
Regards Chris
The length of the run is 8 metres and there is a 30ma rcd in the consumer unit
Regards Chris
Hi Chris - site unseen that doesn't sound like something an Electrician would say as an 8.5kW shower is not normally connected by flex. Certainly not a kettle flex as they will be rated about 3kW max.
Your electrician is absolutly wrong
8500w @ 240v = 35.4A
or even
8500w @ 230v = 36.9A
so 32A is not sufficent.
40A would be minimum.
What electrician in his right mind would hook up a water heater
without knowing for sure it's ratings ?
Scheer madness.
Think the OP said his electrician said the ‘cooker’ should be connected with flexible cable?
I think your electrician, might be referring to the final connection between the house fixed wiring (cooker outlet plate) and cooker appliances. Some manufacturers provide specific leads, some electricians will use a suitably sized heat proof etc cable, but in some cases, a twin & earth cable would suffice. Most cooking appliance are fixed into position and are hardly ever moved. For comparison, a commercial oven, would need a suitable flexible cable, as it would be moved regularly for cleaning. Well most good kitchens would be cleaning behind it!
Regards Chris
He could have used 6mm flexible cable or 6mm T&E cable, assuming that 6mm is the correct size. Either is perfectly acceptable as long as it is correctly installed.
I think this electrician needs to brush up on their knowledge of the regulations!
and maybe retrain as a plumber. they ain't got a clue about electrics anyway, so he should feel at home.
He also said that the 40 mcb for the cooker should be changed to a 32. As I understand it the principal of diversity could be applied so that could be ok but would a 40 mcb with a 6mm cable over a 7 or 8 metre run be dangerous clipped direct not in insulation?
It is just a standard cooker grill, oven and 4 rings.
Reply to Shower 8.5 on a 40mcb is it dangerous in the UK Electrical Forum area at ElectriciansForums.net
Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Hi all. Sort of an interesting one. I had a call from a client to say she is getting a shock when using the shower. I told her not to use it and...
Hi guys. I was wondering what size cable and braker I'd need for an electric shower. Just out of intrest am I close in guessing as follows: The...
  • Locked
My house was built in the 1930s, The fuse in my service cut out is 60Amp and the wire coming from the street has a 16mm2 copper core(easy to see...
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...